Steel roof deck on glulams
We're working on a project that's just in schematic design and the architect wants to look at using glulam beams combined with a 3" metal roof deck (glulam spacing will be about 8'-0" on-center). The framing at the perimeter of the roof will be steel beams, not wood; i.e. the glulams are just the "interior" beams. I'm taking a look at the diaphragm capacity tables which of course are based on support fastener spacing, sidelap spacing, and deck span. It doesn't say specifically in the tables that the deck supports are to be steel. I'm thinking that as long as I specify wood screws with an embedment into the glulam that can develop similar uplift capacities as a tek screw, then the diaphragm shear values should be similar. Based on my understanding, the diaphragm connections are most critical along the perimeter of the roof (where we will have steel) and the diaphragm anchorage to the glulams would be to resist uplift and buckling of "deep beam" diaphragm. Any thoughts on this approach?
RE: Steel roof deck on glulams
Next has to do with material compatibility, fastening and inevitable roof leaks. When you fasten light gauge steel to wood, they must be isolated from each other. You will have moisture absorption in the wood which will corrode the steel with time, even on the interior. This condition is exacerbated where fasteners penetrate the decking into the wood. Since fastening will be done in the bottom of the flutes, water from roof leaks and condensation will collect there and have a path to the wood, leading to deterioration and loss of fastener shear and uplift capacity.
Think beyond the overt structural design and consider serviceability and long-term efficacy.
The second point is an interesting one, however the deck is being covered with recovery board, polyiso insulation, and membrane. It won't be exposed deck. The decking and anchors will be galvanized to limit deterioration, but perhaps we should specify stainless steel screws?
The screws should be corrosion resistant, either galvanized, cadmium coated or stainless. I can't see any need for a separator between the deck and the glulam.
BA
Logically, I agree completely. Between boundary members, the diaphragm fasteners perform these following functions as you've suggested:
1) Uplift resistance which should be no problem.
2) Panel to panel shear transfer which should be largely unaffected by substrate.
3) Bracing against panel shear buckling which should be no problem.
My only concern would code compliance. Not sure if you're drifting off reservation with respect to ICC reports etc. Might be worth a call to Vulcraft etc.
I have walked on top with the 200 lb owner and it is extremely stout (meets code too)
The SDI construction span is 16'-6"
Not sure why he is so excited.
Here is my personal pole barn using the same decking. It really makes an efficient system.