STRAP FOOTING
STRAP FOOTING
I am designing a corner footing supporting a three-storey steel building. Steel columns are supported by concrete pedestals. Three pedestals sit on the property line which calls for 'strap footing' as a solution. I have some references that deal with such footing but they don't have one which involves moments (DL, LL, ME).
It will really be helpful if anyone can share with me a manual solution.
Thanks a lot for any help.
RE: STRAP FOOTING
RE: STRAP FOOTING
Mike McCann, PE, SE (WA)
RE: STRAP FOOTING
DaveAtkins
RE: STRAP FOOTING
I've not seen an example of this in print either. I would:
1) Add the column moments and shears to the grade beam and track the loads through and;
2) Give some consideration to the rotational restraint that the strap beam will or won't provide to the column as that will impact drift and first story stiffness.
RE: STRAP FOOTING
Yes, the strap acts as cantilever beam to transfer some loads to the interior column.
If there have been axial loads only, it would have been easy to draw the S&M diagrams.
Calculated loads are P(ext) = 239kN, P(int) = 444kN, M(ext)=51kNm, M(int)=103kNm.
Please show me a solution at your convenience.
RE: STRAP FOOTING
1) Add your two moments together for the direction considered.
2) Divide the sum by the distance between footing centroids to get the additional overturning reactions, associated footing bearing pressures, and associated uniform loads exerted by the footings on the strap beamfor this component of the load.
3) Create moment and shear diagrams for the strap including the effects of the concentrated column moments and the uniform footing loads from #3.
4) Add the moments and shears from #3 to the moments and shears that you would have had without the moments applied.
Can you provide:
1) distance between columns?
2) distance between footing centroids?
3) direction of frame shear for case considered?
4) depth of strap beam?
The column shears technically affect strap moments, shears, and axial forces too but that affect should be fairly minor.
RE: STRAP FOOTING
2. Centroid Xbar=2.502m
3. East to West (not really understood)
4. Strap beam depth h=380mm
Can you please illustrate the steps given above that involves moments.
RE: STRAP FOOTING
RE: STRAP FOOTING
RE: STRAP FOOTING
RE: STRAP FOOTING
I tried to draw the shear and moment diagrams but they do not end at zero.
Please see the excel file at your convenient time.
RE: STRAP FOOTING
RE: STRAP FOOTING
Now, I am bit confused on how to transfer some load to F2 (int) since P2 isn't included?
How do I determine the dimension of F2 and the forces to determine reinforcements?
RE: STRAP FOOTING
RE: STRAP FOOTING
Will F1 be provided with top steel parallel to the strap? or the negative moment is all carried by the strap beam and thus F1 doesn't have to carry any negative moment.
RE: STRAP FOOTING
This exactly. That is, of course, unless you're countie on tie down force from the footing when the moments are reversed.