NYC Booster Pump vs. Fire Pump for Combination Standpipe Systems

NYC Booster Pump vs. Fire Pump for Combination Standpipe Systems

(OP)
I have the exact same situation that came up in a previous thread regarding combination manual-wet standpipe systems in NYC. http://www.eng-tips.com/viewthread.cfm?qid=279878

Basically, our building type requires a standpipe system based on floor area sizes (not a covered mall). It is a low-rise structure so manual-wet is the minimum requirement for the standpipe system. We are utilizing a combination sprinkler/standpipe system but require a pump to meet the sprinkler system demand only.

Since the pump is only required to meet the sprinkler system demand, we would like to call it a "sprinkler booster pump" in lieu of a "fire pump" so we can avoid the requirement for two separate water mains off two separate streets. However, there are questions as to whether or not a booster pump can technically feed into a combination sprinkler/standpipe system.

The only water supply requirement for a manual-wet standpipe system other than the FDC is a small connection for the purpose of keeping the pipe filled with water. Obviously, a booster pump will achieve this requirement and since the pump has a bypass, it will keep the standpipes filled even if the pump ever goes down.

Has anyone ever ran into this situation before in this jurisdiction? Can you have a combination manual-wet standpipe system supplied from a sprinkler booster pump with a single underground supply line in NYC? Or, will this "pump" need to meet all the "fire pump" requirements which includes two separate undergrounds from two separate streets?




RE: NYC Booster Pump vs. Fire Pump for Combination Standpipe Systems

No experience in NYC, but I have done this on several different projects not in NYC. It is still a UL Listed fire pump. But lets say the sprinkler demand is 300 gpm and the standpipe is 1000 gpm. I have put in a 300 gpm pump many times. You just upsize everything once you get to the point where the standpipes are.

Travis Mack
MFP Design, LLC
www.mfpdesign.com
"Follow" us at https://www.facebook.com/pages/MFP-Design-LLC/9221...

RE: NYC Booster Pump vs. Fire Pump for Combination Standpipe Systems

(OP)
Thanks. That is the frustrating part. There is physically no difference between a "fire pump" & a "booster pump". The only thing that differentiates them is which system they serve. A "fire pump" implies that there is an automatic-wet standpipe inside the building so FDNY doesn't need to pump in through the FDC to meet the standpipe demand. A "booster pump" implies a manual-wet standpipe which tells FDNY they do need to pump in through the FDC to meet the standpipe demand.

It truly is a matter of semantics but it can have huge repercussions on the basic requirements for the system (i.e., two underground lines from two city streets). In any other jurisdiction, a pump serving a fire system is a "fire pump" but that is not the case in NYC; for whatever reason the differentiate between a booster pump & fire pump.

I was hoping that someone with experience in NYC would be able to answer whether or not a "sprinkler booster pump" could supply a combination manual-wet standpipe system or not.

RE: NYC Booster Pump vs. Fire Pump for Combination Standpipe Systems

Interesting the terminology.

I learned, and still say, A "Booster Pump" connects to a city supply.
A "Fire Pump" is fed from a tank.

Guess NYC has different meaning..

R/
Matt

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close