Mv cable screen

Mv cable screen

Mv cable screen

(OP)
What would be the implications of not bonding an mv single core cable screen at all? Dont intend to do this but am trying to understand what consequences would be if this inadvertently happened. Would it be a concentration of electrical stress on the insulation at the isolated screen ends and/or noise would be greatly annenuated due to unterminated screen resistance.

RE: Mv cable screen

The outer sheath would effectively become part of the active insulation system instead of being decoupled from the it by the earthed screen, subjecting it to voltage stresses it is not designed to handle. The screen would be at a non-zero potential determined by the capacitances and leakage resistances of the screen to the sheath and screen to live conductor. At terminations you may find that local electric field strengths exceed design values and PD occurs.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources