3ph 208v Power Supply using a VFD on 230/460 Inverter Duty Baldor Motor

3ph 208v Power Supply using a VFD on 230/460 Inverter Duty Baldor Motor

3ph 208v Power Supply using a VFD on 230/460 Inverter Duty Baldor Motor

(OP)
Hello,

I have 3ph 208v power supply and am wondering if I can use a VFD that i currently have on a new Baldor motor that is rated 230/460v. Do i need a 208v rated motor or can the drive work with the 230/460v inverter duty motor?

Adam

RE: 3ph 208v Power Supply using a VFD on 230/460 Inverter Duty Baldor Motor

You don't say the size, but as a gross general rule, most SMALL motors rated for 230V will be OK with 208V, Baldor even has a White Paper saying that, defining "small" as 5HP and below (IIRC). But that is predicated on allowances in the motor frame for the added heat. Running on a VFD also adds heat, so I would say either/or, not both.

Instead of changing the motor, I would just get a simple buck-boost transformer ahead of the VFD and put 240V into it.


"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington

RE: 3ph 208v Power Supply using a VFD on 230/460 Inverter Duty Baldor Motor

If you provide a serial number or model number I can tell you if the motor is rated for 208V.

RE: 3ph 208v Power Supply using a VFD on 230/460 Inverter Duty Baldor Motor

FYI, the paper I was referring to:
http://www.baldor.com/Shared/manuals/pr2525.pdf

The part about 208V on 230V motors is on pdf page 60.


"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington

RE: 3ph 208v Power Supply using a VFD on 230/460 Inverter Duty Baldor Motor

AKA The Cowern Papers. An all-around good reference for motors. lps

Bill
--------------------
"Why not the best?"
Jimmy Carter

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources