3ph 208v Power Supply using a VFD on 230/460 Inverter Duty Baldor Motor
3ph 208v Power Supply using a VFD on 230/460 Inverter Duty Baldor Motor
(OP)
Hello,
I have 3ph 208v power supply and am wondering if I can use a VFD that i currently have on a new Baldor motor that is rated 230/460v. Do i need a 208v rated motor or can the drive work with the 230/460v inverter duty motor?
Adam
I have 3ph 208v power supply and am wondering if I can use a VFD that i currently have on a new Baldor motor that is rated 230/460v. Do i need a 208v rated motor or can the drive work with the 230/460v inverter duty motor?
Adam





RE: 3ph 208v Power Supply using a VFD on 230/460 Inverter Duty Baldor Motor
Instead of changing the motor, I would just get a simple buck-boost transformer ahead of the VFD and put 240V into it.
"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington
RE: 3ph 208v Power Supply using a VFD on 230/460 Inverter Duty Baldor Motor
RE: 3ph 208v Power Supply using a VFD on 230/460 Inverter Duty Baldor Motor
http://www.baldor.com/Shared/manuals/pr2525.pdf
The part about 208V on 230V motors is on pdf page 60.
"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington
RE: 3ph 208v Power Supply using a VFD on 230/460 Inverter Duty Baldor Motor
Bill
--------------------
"Why not the best?"