Maximum continuous operating voltage and equipment selection
Hello all,
I'm working for a Canadian engineering company, and I have encountered a number of times where the maximum system voltage is 253 kV (or 1.1 x nominal voltage [230 kV]) and we always seem to get into a discussion if the equipment, which is usually built and tested for 242 kV and 245 kV (IEC), is suitable for use at 253 kV. I've had cases where we need to provide cables, sealing ends, and disconnect switches rated to 300 kV (next IEC class). The same topic has come up with lower rated gear, but this goes into the realm of type testing, which most companies have not done for this voltage or won't do it without considerable cost!
What would be the general approach to this? I've had instances also where a certain GIS cable sealing end vendor certifies their GIS sealing ends to 253 kV, but it is tested formally to 245 kV, and they certify the max voltage via a signed letterhead with statements providing the standard hi-pot test voltages. But I've also had cases where the same vendor provided confirmation that their cable is rated to 253 kV when using ICEA standards , but the same cable would need to be upsized to a nominal voltage class of 300 kV when using IEC standards. And one other thing, the GIS manufacturer has tested to 253 kV, but the gear is rated at 230 kV and has a nominal MCOV of 245 kV!
This has considerable cost implications for various projects and it seems the unharmonized standards are a culprit here.
Care to share your thoughts and experiences?
RE: Maximum continuous operating voltage and equipment selection