Aluminum embedded in concrete (yes again)
I provide engineering services to a stair and railing manufacturer in the Midwest. I was researching the concerns of embedding an aluminum post into a high-strength non-shrink grout for a railing application, and I came across many threads discussing the matter. However nowhere did any of the posts (that I could find) discuss powder coating of the aluminum. According to the Aluminum Design Manual 2010, M.7.3 states "Aluminum shall not be embedded in concrete with corrosive additives such as chlorides if the aluminum is electrically connected to steel. Unless the concrete or masonry remains dry after curing and no corrosive additives such as chlorides are used, aluminum surfaces to be placed next to or embedded in concrete or masonry shall be:
a.) given one coat of suitable paint....or
b.) given a heavy coating of alkali-resistant bituminous paint or
c.) isolated with a suitable plastic tape or other isolation material.
Wouldn't powder coating of the aluminum be a sufficient barrier? Also in the case of an aluminum railing post, I read that an epoxy grout was recommended because it is less harsh than the concrete. I need to research the specific mix more closely, and I don't disagree that it is not an ideal situation, but I don't see anything that discourages embedding aluminum in concrete.
I am a simple structural engineer and don't pretend to be a chemist or corrosion engineer, so your thoughts and experiences would be welcome.
N8structural
RE: Aluminum embedded in concrete (yes again)
Can snow and salt get piled against these?
If so then are you willing to bet that your coating stays intact during installation?
Powdercoating meets condition a). Whether that is suitable for your application is unknown.