Calculating Embedment Depth of Pile ?
Hi there,
A marine beacon (in this case pile with a sign on it used to signal ships) has been designed by a previous structural engineer in my department in the past (he no longer works at the company). The project manager has asked me if it would be fine to alter the marine beacon design by reducing the embedment depth from 25 feet to 20 feet (this is mainly because we have left over 20’ piles from a previous project and the P.M. did not want to waste money welding another 5’ of steel on.). The marine beacon is embedded into coral reef. The pile is a 2.5’ diameter steel pile filled with concrete.
I am a graduate and not fully confident in pile design. I did approach the senior structural engineer. He initially did not want me to do this project because of the amount of geological unknowns. However, he told me to try it and if I can convince him then we will agree with the proposed changes.
I have used the rigid analysis formula for piles and posts for signs embedded in the ground, where lateral loads govern from the international building code IBC 1805.7.2 as seen in my Foundation design book by Coduto. Please let me know if I am going about this in the right way and if my assumptions are suitable.
The first thing I determined was the wind loading – See attached image of calc:
**I do not know how to determine wave loads (I do have data on the wave speeds and heights but do not know how to actually get a wave loading figure). Because of this I assumed worst case scenario hurricane force winds of 150mph with a safety factor of 1.5 acting down the length of the pile (i.e. neglecting the wave loads and assuming 150mph*1.5 winds are acting on the length pile above the reef, which is 20’. In the country where I reside, we do get hurricanes up to category 4, is this assumption reasonable?
I next used the rigid analysis formula to determine the minimum embedment depth. – See attached image of calc:
For this calculation because we did not know the condition of the reef (normally it would have the strength of sedimentary rock), I assumed that the soil conditions were sand.
With this said I ended up getting a minimum embedment depth of 15. 2 feet, which would mean that reducing the embedment depth from 25’ to 20’ should be fine.
What are your thoughts? Any guidance would be greatly appreciated.
RE: Calculating Embedment Depth of Pile ?
The wave load could definitely prove to be critical. I use to do a lot of design work on the Florida cost, and they had a CCL [?] line that if you were in behind it.....you could count on some pretty hefty wave loads. In fact the wave loads are a whole other animal.....under the right conditions, they can give you responses you don't want (dynamically). IIRC, ASCE 7 does currently give static wave loads. If you are working in Florida, I think their building code does too.
While I think it is a good learning exercise, I think you should also consider whether the cost of the engineering vs. the cost of welding a 5 foot extension will result in any significant savings on the project while at the same time increasing risk of something going wrong, especially when there are uncertain geological conditions.
I agree with Canuck65; leave it a 25' Perhaps the previous engineer included an allowance for potential scour?
@Bridgebuster Unfortunately I do not have the previous calculations. I will definitely take a look at the UFC document. Hopefully it will give me the information required to calculate a suitable wave force (I needed to learn how to calculate wave forces for another project also, so that will be a big help). Your point on the potential scour is also a good one. The scour depth is an unknown.
* Another question *
If I calculated the wave load and found that it was higher than the wind load. Could I just apply that wave load on the entire upper section of pile as I was going to do for the wind loads? I ask this because it doesn't seem that the rigid analysis formula accounts for changes in moments due to different loads.
Keep in mind that I'm not familiar with the rigid analysis formula you reference, is it based on broms or similar derivations?
Apply the wave load over height you have waves being applied, and similar for wind. Combine in accordance with the load combinations in you code (there may be additional load factors on the wind or waves that further factor up the loads.
Fatigue may also be an issue that needs consideration with the repetitive loading from waves over the life of the pile.