Another Gauge Problem
Another Gauge Problem
(OP)
Buckeye Macungie Tank Farm, Emmaus, PA
Fortunately nobody was injured or killed and damages were minimal ... this time.
The investigation revealed that the set points of alarms and the tanks gauging system had not been accurately set or checked for at least one year. The tank side gauge and the GSI tracking system were reading about 18 inches lower than actual levels in the tank. The independent Hi-Hi magnetrol alarm level was set 7 inches too high. As a result, the tank gauge was showing the tank level to be at max safe fill at the same time the Hi-Hi alarm was receivedand, however the tank was in an overfill condition.
http://www.phmsa.dot.gov/staticfiles//PHMSA/Pipeli..._[Redacted_for_Internet].pdf
Fortunately nobody was injured or killed and damages were minimal ... this time.
The investigation revealed that the set points of alarms and the tanks gauging system had not been accurately set or checked for at least one year. The tank side gauge and the GSI tracking system were reading about 18 inches lower than actual levels in the tank. The independent Hi-Hi magnetrol alarm level was set 7 inches too high. As a result, the tank gauge was showing the tank level to be at max safe fill at the same time the Hi-Hi alarm was received
http://www.phmsa.dot.gov/staticfiles//PHMSA/Pipeli..._[Redacted_for_Internet].pdf





RE: Another Gauge Problem
RE: Another Gauge Problem
While the NTSB never actually concluded that someone had deliberately disabled the stall warning system by flipping off the circuit breaker controlling this system, after the crash there were several reports from unnamed pilots who stated that on occasion people had turned-off the audio warning systems simply because many pilots considered them to be unnecessarily redundant and a big PIA.
https://en.wikipedia.org/wiki/Northwest_Airlines_F...
Note that I was living and working in Detroit at the time of the crash and that I had on occasion taken that same NW flight to Orange County as our primarily development office was located there, where I had worked from 1980 thru 1985 and where I worked after I went back to SoCal shortly after this accident took place.
John R. Baker, P.E. (ret)
EX-Product 'Evangelist'
Irvine, CA
Siemens PLM:
UG/NX Museum:
The secret of life is not finding someone to live with
It's finding someone you can't live without
RE: Another Gauge Problem
Keith Cress
kcress - http://www.flaminsystems.com
RE: Another Gauge Problem
Main Point of the report was even if you install it, it needs proper maintenance and operation.
Design engineers tend to ignore that aspect of their work. Simply specifying that something be installed doesn't necessarily mean a peaceful eternity.
Here's the page with all the recent reports,
Maybe we can find it again.
http://www.phmsa.dot.gov/pipeline/library/reports/...
RE: Another Gauge Problem
http://www.phmsa.dot.gov/staticfiles/PHMSA/Pipelin..._[Redacted_for_Internet].pdf
RE: Another Gauge Problem
RE: Another Gauge Problem
RE: Another Gauge Problem
RE: Another Gauge Problem
TTFN (ta ta for now)
I can do absolutely anything. I'm an expert! https://www.youtube.com/watch?v=BKorP55Aqvg