Dear Experts,

i want to know the way of contactor sizing of dahlander motor. the motor is variable torque type.
thanks in advance.

RE: Dahlander Motor

Size the contactors according to the current which will flow in them. If the contactors are IEC types then the AC-3 rating is the one to use, unless you're doing something more severe like inching or plugging which would take it to the AC-4 or AC-5 rating.

Hint: the low speed contactor is sometimes smaller than the high speed and shorting contactors, which are normally of equal rating.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources