Two Stage Seismic Approach - Building Period
When using a two stage analysis procedure for podium buildings, what do you use to calculate the period of the lower level.
It seems if you used the two stage approach and designed the lower level using the period based only on the number of lower floors (using the approximate period equation) you would get excessively high shears at the lower levels. This is because your period would decrease which increases your Cs. Then you are taking the reactions of the upper floors and scaling them based on R/p. This would give you much higher shears than if you considered the entire building as one unit and took the worst case R/p.
Any thoughts here?
Thanks!
Any thoughts here?
Thanks!
RE: Two Stage Seismic Approach - Building Period
Something fancier than than the simplified equations based on building height. Software, Rayleigh method...
Higher, lower level diaphragm contributions to storey shear. Not necessarily super high storey shears as much of that load is aggregated over the whole height of the building including those more flexible levels. And it's right that your diaphragm contributions below grade will be high. Usually the below podium structures are pretty damn rigid. Often you'll be on the constant acceleration plateau and relatively insensitive to precise period determination.
But yeah, R/p hurts.
I don't have access to ASCE7 this week but is your choice not between two stage and RSA? I'd expect both methods to be about equally punishing which, of course, is the very point of the thing.
In high level terms, I'm a two stage method fan boy. I think that's it's a rational method well suited to the expedidient design of modest podium structures.
EIT
www.HowToEngineer.com