<5% Gravity Alteration
Quick question I have my thoughts about, but got to thinking and wanted to bounce it off the community...
Currently analyzing the addition of some dead load to a roofing system. Want to make use of the <5% increase in demand to make this easy for everyone.
My question...do I compare the new dead load to the overall load (dead, live roof), or only dead to dead...I can see how you could argue both ways in various circumstances...
If we have a system designed for minimal dead but a ton of live or roof live, then a minimal dead load addition would be fine, but maybe not <5% if you only compare dead to dead. On the other hand, if you compare the new dead to everything else, where do you stop (dead, roof live, snow...I personally wouldn't use snow/rain/etc in my capacity)? Thoughts?
Thanks!
Thanks!
RE: <5% Gravity Alteration
At the end of the day, if I compare to Dead+Roof Live I am fine, but if the city rejects me and I can only compare dead to dead...well...no bueno...
I do agree that if I knew what loads were applied, etc, I would use the largest since that is what the system was designed for. But, alas, was designed and built in the 70's; were aren't sure what the original loading was so I am trying to be very conservative and use as little load as possible for the comparison.
Here is more detail:
Have a truss system in a mall atrium. Owner wants to hang a ridiculously large LED billboard type of sign from the truss system. I have no idea what loads were originally used, so I am trying to use only the bare minimum that will still keep me under the 5% so I can avoid analyzing this roofing system (it's more complicated than just "a truss" as I have let on).
Then look at your new load condition, with that combination, and verify that the total load isn't more than 5% over.
For uniform loads, this can be done by comparing the loads.
For your case, with the new concentrated load you can't just look at loads.
You'd have to look at comparisons of shears and moments to see that you haven't increased them more than 5%.
1. as i understand it, what your referencing says a 5% increase in forces due to gravity loads, not simply a 5% increase in loads.
2. agreeing with others above, worst case seems appropriate, and others observing local vs global conditions.
3. " in a mall atrium. Owner wants to hang a ridiculously large ..." are there people below it?, be careful.
4. "a ridiculously large LED billboard type of sign from the truss system...." sounds like significant point loads on a truss, which "I have no idea what loads were originally used". Suppose the trusses were originally designed for a nice uniform load. It's not unreasonable to anticipate that, although your atrium truss' overall moment capacity and shear capacity remain within our magical 5% envelope, nevertheless, local webs and local web connections may experience design forces exceeding their original design by 100% or 50% or 500%.
5. above was math, now some philosophy. recently looked at a retail store switching out 3 RTUs, "like for like" as the contractors like to say. total weight change was from about 1250 lbs to 1350 lbs each. problem was, roof designed originally for only 2 RTUs at 1250 each. someone had installed a 3rd sometime back when, unengineered and unpermitted. The replacement of the 3rd RTU could have been justified in the present based upon the 5% related to 'existing' 1250 lbs, but not 5% related to 'original' 0 lbs.
6. 5% increase ok, but what about when the allowables are less today than we thought back then, like bottom chord tension in a bowstring truss? by the way, what material is your truss made of? Then there was the in-grade lumber testing propgram that adjusted lumber allowables again.
7. a steel truss roof was just installed but unoccupied when the owner wanted to add some RTUs. The design engineer, who had exact knowledge of design criteria, wanted to use the "5% rule". Somehow I think that this was not the intent of the 5%, but rather perhaps to give engineer's some room to exercise sound engineering judgment for buildings whose past is shrouded.
1) hang from the truss panel points.
2) make a reasonable estimate of your loads.
3) pick a sensible load case for comparison. Probably just 1.25D + 1.50L.
4) work out your truss shear and bending diagrams.
5) work out your truss shear and moment diagrams with the new load included.
6) Ensure that your shear and moment diagrams have nowhere grown by more than 5%
The trouble with a truss will be, if your new loads occur near med span, your original shear diagram may take on a rather low values there which could neuter the efficacy of the 5% method in that area.
If you are curious still, in this instance, the truss span is 80'. It is actually two trusses side-by-side that are low...Altogether, we have roof trusses spanning 80' @ 10' o.c. bearing on two lower 80' trusses that run orthogonal.
All members are 5-1/8" x 21" glulams, with joints every 10'. The sign will hang from these two glulams (one each truss) at midspan of the 80', but will mount near the joints, so the induced moment and shear on the chord it is actually hanging from will be very small - all of the load will (almost) be imparted to the nodes, so that's good news...
Anyway, thanks for the insight here! I love this place.