(OP)
Around 10 photovoltaic solar panels fixed on AL structure is installed ground loop. Another ground loop is 100ft away around control house where are installed AC and DC O/C and surge protection.
These two loops are connected with two conductors creating third loop.
My manager is suggesting :
1. Connect to the first ground loop two lightning rods
2. Connect to the same ground loop - common bonding bus where are connected (a) metal supports of solar panels (b) metal PV solar frames (c) metal protection boxes ( for surge protective devices).
3. Create another common bonding bus at control house where are coonected main surge protective devices

Can I mix lightning protection and bonding on that way. Can I create a common point for solar panel metal supports and SPD - surge protection device metal boxes before I go to the grounding.
My answar is NOT. Maybe I am wrong

RE: Lightning Grounding and Bonding

In my opinion, you may bond all grounding means together as per NFPA 2011:
chapter 4.13 and 4.14.
4.14 Common Grounding.
4.14.1 General. All grounding media and buried metallic conductors that can assist in providing a path for lightning currents in or on a structure shall be interconnected to provide a common ground potential.
4.14.1.1 This interconnection shall include lightning protection, electric service, communications, and antenna system grounds, as well as underground metallic piping systems.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources