Hello,

I have a composite column CHS900x40 that needs to be protected for 2 hours.
The calculation method exposed on Eurocode is not applicable for columns with D>400mm. The solution proposed by the EC is either protect the steel for T=350°C or do a thermal calculation (fancy software). I've been told by some fire experts that the behavior of a composite column under fire is such as the increase in the steel is slower and maybe won't activate the chemical reaction when needed on the intumescent paint.

Do you know an intumescent paint for composite columns that is able protect for 350°C?
Does AISC or other codes give some guidance on this subject?

Thank you very much

RE: Composite column - Fire protection 2 hours - Big diameter D=900mm

(OP)
Well, I talked to 2 fire design experts and I learned 2 things:

- It's unsafe to calculate the resistance of the column under fire by ignoring the concrete. Because the loads under fire are less important, I though than maybe I could check for steel only, but it's an unsafe approach because of "the unequal temperature field creates a rather inhomogenous distribution" and "the unequal temperature field leads to strong internal stresses" ( see Technical note #55 of ECCS)

- In eurocode, for big columns (diameter>400mm) I have to check with a lab or run a thermal calculation

RE: Composite column - Fire protection 2 hours - Big diameter D=900mm

Thanks for the follow up!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources