Issue ESFR sprinklers in standard rigid metal frame and 8" bent metal purlin building

Issue ESFR sprinklers in standard rigid metal frame and 8" bent metal purlin building

(OP)
I already know the answer I need to ask again for a specific job.

Bent metal purlin building measuring 150'-0 wide by 266'-8 long with bays spaced at 25'-0" except for the two end bays that measure 20'-10" which brings us to the overall length of 266'-8".

Building has a 31'-0" eave which gives us a peak of 37'-3".

Rack storage of Class IV products and un-expanded plastic with the owner telling me the maximum height of storage will be 20'-0".

With the water supply being what it is an ESFR system with a fire pump is the only option.

With 25'-0" bays I space the ESFR sprinklers 8'-3" apart and I am never allowed to be closer than 8'-0" even if there is a rigid frame separating the sprinklers. If you have a 48" beam you are allowed to space sprinklers 2'-0" apart if you want as long as the beam separates the sprinklers but this is not the case when it comes to ESFR sprinklers. Whether the beam is there or not the minimum distance between sprinklers remains at 8'-0".

Where did I get this information? Six years ago I was taking a 4 day CEU class to maintain my NICET and in one of the classes given by Kenneth Isman, specifically having to do with ESFR sprinklers, he asked that particular question and 80% of us got wrong. We were told it had something to do with the heat plume (I think it was carrying water droplets to the near head) and it is something I always followed.

So what I can do is space heads 8'-0" apart with the line nearest the end bay 1'-10" off the end wall then 8'-0" until I can space 8'-4" again.

Thing is I know I am going to run into a problem getting some people to accept the fact this is the only way to do it or maybe something changed from six years ago?

RE: Issue ESFR sprinklers in standard rigid metal frame and 8" bent metal purlin building

I've always done it your way as well. Have been yelled at quite a few times when I point out that a baffle can't be used in lieu of the minimum 8'-0 spacing for ESFR sprinklers. FM Global gets pretty sticky on minimum spacing as well, especially when they impose a minimum area, not just minimum spacing. Sometimes it is as close as max area = 100 sq. ft, min area = 80 sq. ft. Those are tough layouts.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close