2LG fault from utility and ETAP doesn't match?!

2LG fault from utility and ETAP doesn't match?!

2LG fault from utility and ETAP doesn't match?!

(OP)
Guys,
for a 2LG fault in phase A and B, fault current flowing to the ground should be calculated as:
Ifground=IfA+IfB.
I have IfA and IfB separately from utility but, summing them up, gives a (smaller) number which is not matching ETAP.
Is this because ETAP only gets single and 3phase short circuit parameters for utility and its 2LG current is not correct?
Or, may be there is something that I am missing here?

RE: 2LG fault from utility and ETAP doesn't match?!

(OP)
I talked with ETAP and like to share what we found out:
For 2LG faults ETAP report shows the largest current among phases (not the current going to the ground).
This is important for grounding grid design because, we should know Max(1LG and 2LG).

RE: 2LG fault from utility and ETAP doesn't match?!

If the equivalent grid [Utility] shown impedances are the actual then the shown currents are correct calculated -by Utility[ 1.03 factor it is used to enhance the voltage].
ETAP calculations-if Bus 4 data are the results-are not based on these impedances, in my opinion.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources