Connections between Ground wire and Neutral wire in 3 Ph 4W System

Connections between Ground wire and Neutral wire in 3 Ph 4W System

Connections between Ground wire and Neutral wire in 3 Ph 4W System

(OP)
Hi,
In 3φ4W power system like 208/120V and 416/240V, G and N wire need to take care.
There are 4 connection cases between G and N wire as attached.
Please advise which one is practice connection and their pros and cons.
Any guideline or article that I can refer to ?
Thanks for your advice.
Have a Nice Day.

RE: Connections between Ground wire and Neutral wire in 3 Ph 4W System

Case A is very poor practice. One of the purposes of grounding is to develop fault currents sufficient to trip the protective devices. In basic systems without ground fault interruption this would be the circuit breaker. Case A does not provide this protection.

Case B is the typical connection for sub panels in a building. This connection may be used when the transformer is consumer owned rather than utility owned.

Case C is the most common connection. The utility provides a ground connection at the transformer and there is a connection between the neutral and ground at the main service panel. This connection may also be used for sub panels located in another building.
Historically one conductor was used as both ground and neutral for large appliances in the US. This would be electric ranges and electric driers. This use is no longer code compliant.

Case D may be encountered when the connection between the utility transformer is underground. However this connection will often result in part of the neutral current flowing in the grounding conductor. For this reason this connection is avoided. The grounding conductor may be carried with the phase conductors to the panel, but then be not connected to the neutral.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Connections between Ground wire and Neutral wire in 3 Ph 4W System

(OP)
FreddyNurk and Bill, thanks for your reply.

Bill, thanks for your excellent explanation.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources