(OP)


LOADING DOCK
1100 SF
12FT HIGH WALLS
36X30

TWO 12X10 ROLLUP STEEL DOORS

USING ENVELOPE LOADS/ 60DEGF SPACE TEMP

2ACH= 33MBH UNIT HEATER
4ACH= 56MBH UNIT HEATER

30 BTUH/SF OR 50 BTUH/SF, WHICH IS BETTER
THE DOORS WILL OPEN DURING DELIVERY AND WILL NEED TO HEAT UP QUICKLY WHEN GONE.

TWO HEATERS OR ONE WILL BE BETTER?

RE: LOADING DOCK

1st. watch caps lock, conveys SHOUTING.

To your question, it depends. Where are the doors relative to each other? Relative to the space (along long or short wall)?
What type of heater(s) are you going to use?
What does your budget allow?
What does the client want/need?
How much space is available? Watch for conflicts with lights, structure, fire protection.
Where/how is product being stored/staged on the loading dock?

Evaluation of these questions and others have to be taken into consideration; it is your job to evaluate different options along with each option's pros and cons.
I could make one or two heaters the better option depending how the above questions are answered.

RE: LOADING DOCK

"Will need to heat up quickly when gone"

"One heater or two, 30btu/sf or 5- BTU/sf"

I think you've answered your own question.

You can always turn one off if it gets too hot.... but it's difficult to turn it up if its not there.

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

RE: LOADING DOCK

Put air curtain type door heater above each door. Available electric, hot water or steam. Call for control panel and space temperature sensor control to energize unit on call for heat even if doors closed. Coordinate door design to clear air curtain door heater.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close