Guys,
I am trying to use a X/R for my utility in ETAP. I have a report from utility guys that shows 4 different X/R for 4 different faults:
LL Fault X/R=4.64328
1LG Fault X/R=1.50927
2LG Fault X/R=3.31539
3LG Fault X/R=4.64338

Which one do you think I should use?

RE: X/R for utility

ETAP only lets you enter the 3LG and 1LG fault information - that should be good enough for most studies, depending on what you are trying to do.

RE: X/R for utility

EasyPower only requires X/R for 3ph and SLG with the corresponding fault current value. I suspect this is typical for most software programs as between the 3ph and SLG faults you should have most of what is needed for a study

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources