(OP)
Gents

if the proposed transmission line is at high altitude area (more than 2000m above sea level) with a span of 300km, 345kV..by simple high level analysis, what are the considerations to be made in design to minimise the line cost in terms of insulation voltage levels?

thanks,
Danilo

RE: Insulation Level

Considering that the altitude derating factor at 2000 m is around 90%, the standard 345 kV dielectric design parameters of the T. Line should be compensated around 10%. This will impact the number of insulators, minimum sag, the phase-to-phase and phase-to ground clearances.
Standard tower design for 400 kV (or 500 kV) at sea level might be used for this application.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources