ASCE 7-10 Risk Category for Wind Turbines?

ASCE 7-10 Risk Category for Wind Turbines?

ASCE 7-10 Risk Category for Wind Turbines?

(OP)
Can wind turbines placed in a rural setting be considered risk category I per ASCE 7-10? The loss of a turbine does not pose a major threat to human life and they do not contain hazardous material in any substantial quantity.

RE: ASCE 7-10 Risk Category for Wind Turbines?

From a life safety perspective, I'm on board with you.

I'd also consider whether the utility is relying on the renewable energy generated to meet any sort of legal quota, and what their replacement lead time is for the nacelle... two other types of risk that may drive the decision even if risk category I is allowable.

RE: ASCE 7-10 Risk Category for Wind Turbines?

Does ASCE 7 even apply to wind turbines? I would assume the wind design for them would be rather extensive, and either in some other document or proprietary.

RE: ASCE 7-10 Risk Category for Wind Turbines?

(OP)
Its not just for wind; the risk factor also applies to snow and seismic.

RE: ASCE 7-10 Risk Category for Wind Turbines?

I worked for an electric utility. For new electric generating stations, I assigned risk category IV for base-load units. Other units, which would include wind turbines, were risk category III.

www.SlideRuleEra.net idea
www.VacuumTubeEra.net r2d2

RE: ASCE 7-10 Risk Category for Wind Turbines?

Wind turbines are outside of the design requirements of ASCE 7. The manufacturer will provide you the maximum and minimum reactions and moments, fundamental period, and soil stiffness required for the foundation, so that the entire unit will operate outside of the critical fundamental frequency range. Depending on the tower height, the foundation may be an octagonal mat, drilled piers, or driven piles.
Dave

Thaidavid

RE: ASCE 7-10 Risk Category for Wind Turbines?

https://en.wikipedia.org/wiki/IEC_61400

I note that according to the Wikipedia article, that fatigue due to turbulence is one of the major design considerations.
Note that in general, ASCE 7 doesn't cover moving machinery.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources