High DGA
High DGA
Hi All
we have two identical generators transformers 420MVA(18/220kV). both transformers has almost the same service time 14 years and got high DGA and buchholz alarms one year in between.
both transformers are currently under inspection by OEM and initial findings were burnt cable in phase -W- HV leads to OLTC at 10CM distance from the HV winding.
another two similar transformers are still in service with almost the same operating conditions and service time.we are concerned if the in service transformers will suffer the same issue shortly. The routine DGA we do every six months and results comes clear for the in service transformers . the two faulty transformers most recent DGA before the failure were also normal one or two months before the buchholz activation.
are there other recommended tests should we do to predict this type of failures,noting that we do tan delta, DC resistance, turns ratio every year and results come normal?
due to long down time to repair any of the two faulty transformers, and considering long lead time to get new transformer, may an expert advise me the fastest way to find similar capacity transformer to minimize the shutdown time?
RE: High DGA
As for finding a transformer quickly, you need to be looking at the surplus market for a similar transformer unless you want to pay up front for a spare you will hopefully never need to use. You'll need to make some effort to preserve the spare transformer in a serviceable condition too.
RE: High DGA
You've listed most of the easy/productive tests.
The only other things that come to mind are
- if you don't install a hydran as per Scotty's good suggestion, consider increasing the frequency of your oil sampling
- Depending on what you know about the cause, I imagine eventually you'll want to drain the tank for internal visual inspection or correction? In the meantime also possibly increase the frequency of outages for off-line electrical testing.
- external thermography - we have been able to see high resistance contacts in LTC comparment this way. Ordinarily we don't hope to pick up anything on the outside wall of the big main tank that might indicate localized winding heating, but if you know exactly where to look based on those other transformers, then you might study for small changes/deviations (especially comparing against similar transformers or trending over time). Also you never know there might be some other indirect clue about transformer condition in infrared thermography.
(2B)+(2B)' ?
RE: High DGA
RE: High DGA
Adding the online DGA to the transformer for the second half of the transformer's life as it increases in failure probability is great plan. Since the online DGA units have a much shorter life span than transformers, we are now specifying that all new transformers have appropriate fittings & valves for DGA but not actually installing the DGA units. For the online DGA units we did install, a huge cyber security challenge was to quickly get the data into the hands of someone both qualified and authorized to remove the transformer from service.
RE: High DGA
RE: High DGA
i attached some photos for the first faulty transformer findings during inspection by OEM who recommended insitu repair after skidding out for 2 m to enable de-tanking.Root cause not yet identified by OEM.
The second faulty transformer not yet inspected.
DGA results by OEM two weeks before the failure shows all gasses are normal but DBDS 200ppm. is it significant?
please have a look on the two DGA results two weeks before the failure and after the BUCHHOLZ activation and shutdown.
your thoughts will be highly appreciated
RE: High DGA
Since DGA did not reveal any abnormality before failure, there is no point in going for Hydran or any other on line monitoring. First point, find out the root cause. By this time it should be clear to an expert. Are you sure burning is only outside? Is there a joint in lead ( brazing or crimped) at the position of burning? If so, was it in sound condition? Some thing deep inside? Have you done all LV tests esp resistance, single phase excitation current at all tap positions on the faulty units? If not, it will help in identifying the problem.
RE: High DGA
http://www.netaworld.org/sites/default/files/publi...
(2B)+(2B)' ?
RE: High DGA
ePete,
That's a useful paper. Thanks for the link.
RE: High DGA
The two in service transformers had Irgmet passivator added before 7 years .the passivator content is being analyses every 6 months and still around 60ppm.However ,we are currently analyzing corrosive sulfur and waiting the results.
The OEM is busy detanking the transformer to check the extent of damage.
Do you think the drained oil with high DDBS and DGA can be treated and reused after repair?
RE: High DGA
powerzizo, When you added passivator in two transformers why you did not add it in the other two units. What was the amount of Ergamet-39 that you added initially? 100 ppm? Check the DBDS content in the working transformers with passivator.
The failures from corrosive sulphur is always like this- sudden and with out any indication in DGA. This cannot be forewarned by any of the diagnostic tests known so far. Normally failure will be inside the windings as inter turn faults at the top or bottom of the windings. Interesting point is these failures are seen only in GSU, Reactors or HV DC transformers.
Of course you can reuse the oil from failed units. But you must add passivator before that. But in case you have to use all new windings and insulation ( in case failure is from corrosive sulphur) why don't use good new oil. I had to handle such a case 10 years back. With Ergamet added I could arrest such failures noted in a batch of transformers.
When IEC 60296 -2003 Specifications for Transformer oil was revised in 2012 as ed4.0, under Table 2 -Specifications, it was added "DBDS - not detectable " with test method added. Also clause A2 of standard has to say " The only compound shown so far to be a potential Cu2 S forming agent and to be present in significant amounts in transformer oil is DBDS .Most oils found to be forming copper sulphide contain this substance"
RE: High DGA
That's an interesting observation. Why does the failure occur so rapidly and without any forewarning? Also the last sentence is intriguing - any idea what the unique design features might be that make these types especially susceptible?
RE: High DGA
Why failures in units with constant current loading -I don't know. I could not find any logical explanation anywhere.
RE: High DGA
RE: High DGA
The two faulty transformers were on the same site, the staff in charge could not confirm that passivator was added. Oil sample from faulty Transformer will be analyzed for corrosive sulfur and passivator content.
Inspection by OEM for both transformer revealed burning cables between the HV windings and the tap changer.The OEM started replacing the cables in the first transformer which already detanked , they told they can repair the second one without skidding out for detanking.
ScottyUK. Would you please explain how to disable tap changing, you mean just not to change the step by OLTC control or we have to physically disconnect the leads ?Apology for my poor knowledge.
RE: High DGA
RE: High DGA
This modification can be done from the tap changer side during shutdown or we will need to drain the oil and do some works from inside the transformer?
RE: High DGA
RE: High DGA
Apology for late update. The transformer repair company has completed the replacement of HV leads to tap changer.according to them the root cause of burning the leads is uneven number of strands in each cable 7 and 14 in addition to poor crimping method.
The trans tanked after repair and moved to its bay.kill filled but unfortunately the Low freq heating machine had breakdown and no other one available. The repair company initially scheduled 15 days for drying with LFH but now mentioned it will take one month because no LFH.is where any other option to expedite the drying.can we back energize the transformer from HV 220kV to work as step down with LV side CB open just to have no load current,if this is possible,should it expedite the draining?
RE: High DGA
Coming to drying-the only way to dry cellulose insulation is by vacuum and heat. In LFH drying, you are able to apply both simultaneously to get very fast drying. No-load current cannot heat anything-it is negligible.Under vacuum you cannot apply any voltage-it is disaster-remember Paschen's law.
To speed up drying,if the following type of heating is applied along with vacuum, it can speed up drying.
(a) put few turns of cable all around outside the tank(touching it) and apply suitable voltage. Eddy currents will appear on tank, heating the insulation from outside.
(b)spray hot oil through sprinklers in to tank with vacuum maintained over it.
Hot oil circulate for 10-12 hours- drain oil quickly, feeding dry air or nitrogen of low dew point say-45C -keep for 12 hours - measure dew point -it will give the moisture level in paper- apply vacuum for 24 hours- oil fill -hot oil circulate
Repeat above cycle for 2-3 times till satisfactory dew point is got.
(a) can be provided through out (b) only during vacuum period
By this way, satisfactory dry=ness will be got within two weeks.
RE: High DGA
Just to clarify,in which condition step a can be provided?and what level of voltage?
RE: High DGA
RE: High DGA
DBDS in all transformers between 100 to 180 ppm-Oil corrosive test was positive, passivator content 35ppm and we will top up to 100ppm.
IS there a standard procedure somewhere for the drying method that you have described?
RE: High DGA
RE: High DGA