Startup overide list
hi all
could someone help me to explain what is Startup override list, and on project what document usually describe it?
regards
haekal
regards
haekal
RE: Startup overide list
So, some of the interlocks, alarms or permissives that are built into the PLC, DCS or hardwire control logic will need to be bypassed or overridden during startup, and then placed back into service once the unit is up and running.
Your company/plant should have a process for such things. Operations needs to be aware of what is overridden before they start and while they are running. The engineer or technician should be very explicit in what work is being performed (or that the process is in startup), and Operations needs to sign each item on the override list and it should be posted. Each item should also have a maximum time that it can be overridden. It can be on a simple excel spreadsheet.
______________________________________________________________________________
This is normally the space where people post something insightful.
Hence a startup list that allows certain alarms and blocks to be bypassed and quenched to get things up and running. They are listed as they usually come from a well thought-out start-up plan that can include many potential problems and disasters if not handled correctly. All overrides would normally be expected to be removed sequentially as the system reaches nominal conditions.
It's usually part of the operations manual. A chapter on start-up.
Keith Cress
Development of these critical documents is mainly the task of the plant process engineer and some input from the plant DCS / PLC controls engineer is also required. In many cases, a great deal of time, sweat and tears involved.