Could somebody enlighten me on the followings:
When samples extracted from the boreholes, their strength was determined by Hand Pentameters. The samples were hard with 4.5+ tsf. This suggests a C = 2250 psf and a bearing capacity of approx. 6000 psf.
However, the clays are moist to dry (summer time) and expected to get wet when it rains and when the moisture increases i would expect a lower C value. How much strength will then the clay have when it gets wet. Thanks.
RE: bearing capacity for clay soils
If you are measuring unsaturated strength, that'd totally affect safe design. Of course, if you really wanted safe design you'd obtain strength using something other than the pocket penetrometer.
f-d
ípapß gordo ainÆt no madre flaca!
You are right that the PPT is not accurate but I can see that the clay samples are excessively hard (measured in the summer). Also after reviewing the local design works, almost all designs used an allowable pressure of 1500 psf. I guess this is because they believe the hard clay materials soften during the rainy seasons. Is this right? But how much softening one could allow by moisture increase?
Using 1500? this seems very off even if the soil is permitted to "wet" during the rainy season - and an assessment of the service limit on allowable bearing pressure (settlement)
I'm just wondering if you are in an expansive soil area of TX .. . they have a lot of problems in some parts of the state.
You are quite right that the question is referred to the expansive soils in Texas. Curious to know how the low bearing capacity that was discussed could be affected by soil expansion. Of course the soil expansiveness would be dealt with swelling and shrinikg parameters as an input to the structural engineer's slab design but those parameters are independent of hearing capacity to the best of my knowledge. Thank you again if you could clarify as I feel I may be missing something important.
I deal with strange perceptions all the time. That said, the shear strength of soil is (almost) always determined in saturated/wet samples. Direct shear test, triaxial strength test (CU-bar) and such are done under saturation.
f-d
This is Professor's Stark website from where you can download his spreadsheet:
http://tstark.net/geotechnical-software
f-d
If the 4.5 tsf clay sample is from the upper 4 or 5 ft, then there's likely a change in moisture during the year and unsaturated strength may be found during the summer - strength that is temporal. At greater depths, there is much less change in moisture and the temporal variability much less.
f-d
Could they be using such low values to ensure a minimum footing width - an intimation of such?? We would, in Toronto, use a minimum 600 mm strip footing width and a 1000 mm square footing width - I realize that for "residences" you could go to 450 mm but 600 is a nice number.