Minimum Shrinkage reinforcement in large culvert

Minimum Shrinkage reinforcement in large culvert

(OP)
Is the minimum shrinkage reinforcement in the most recent version of large box culvert of 150 mm2/m per face of slab low ?

RE: Minimum Shrinkage reinforcement in large culvert

how long is a piece of string?

RE: Minimum Shrinkage reinforcement in large culvert

If the culvert is under a road and designed to the bridge code (AS 5100) then it is required to have 500 mm^2/m in each face minimum, so I'd say the answer to your question is yes.

Doug Jenkins
Interactive Design Services
http://newtonexcelbach.wordpress.com/

RE: Minimum Shrinkage reinforcement in large culvert

(OP)
Thank you Doug. Much difference in minimum requirements from two different Australian standards.

RE: Minimum Shrinkage reinforcement in large culvert

kww2008

Maybe one of those standards is talking about something completely different and is not appropriate for the member you are designing!

RE: Minimum Shrinkage reinforcement in large culvert


Quote (rapt)

Maybe one of those standards is talking about something completely different and is not appropriate for the member you are designing!

... and maybe they aren't.

The AS 5100 requirement is applicable to "All concrete members" ... "with a thickness greater than 150 mm", and a large culvert is a concrete member with a thickness greater than 150 mm.

There is a get out clause:
"The requirements of this Clause in relation to the quantity of reinforcement in a particular
direction may be relaxed if the member is unrestrained against longitudinal movement in
that direction and the effects of differential temperature and humidity are minimal."
but it is arguable that culverts are restrained in the longitudinal direction, at least at the base, and certainly for structures that are in effect culverts, but do not come under the culvert code (such as buried arches), it is standard practice to provide steel to the AS 5100 requirement.

AS 5100 is applicable to:
"Other structures that are required to support road and railway traffic, e.g., culverts
and structural components related to tunnels, except those covered specifically by
other Standards."
so culverts and cut and cover tunnels that do not come under the culvert codes have a significantly more stringent requirement than those that do.

That's an inconsistency with no logical justification.

Doug Jenkins
Interactive Design Services
http://newtonexcelbach.wordpress.com/

RE: Minimum Shrinkage reinforcement in large culvert

Doug,

I meant that the AS3600 minimum reinforcement requirements of about .2% were not comparable to the AS5100 requirements and that there might be a logical reason why. And that reason is partly to do with restraint in this case as per the get out clause logic.

The equivalent rule in AS3600 for restrained slabs would require .6% reinforcement!

RE: Minimum Shrinkage reinforcement in large culvert

I assume we are talking about precast culverts that are 2.4m long.

http://www.nceng.com.au/
"Programming today is a race between software engineers striving to build bigger and better idiot-proof programs, and the Universe trying to produce bigger and better idiots. So far, the Universe is winning."

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close