The Canadian code limits total drift under wind loads to 1/500 of storey height. Does anyone know of any other limit imposed on the deflection of buildings?
Is there any such restriction imposed on deflection due to seismic loads?

RE: wind deflection

Seismic deflection limits are to be found in the NBCC Part 4, in the section on seismic loads. Deflection limits according to clause 4.1.9.2.3) are 0.01hs (h/100) for post-disaster structures and 0.02hs (h/50) for all other structures.

The other limit would be situation specific limitations (for example inter-building spacing that may require more restrictive limits to avoid inter-structure collisions, or communications dish alignment limitations).

RE: wind deflection

dear,,
,,As far as lateral deflection is concerned the BRITISH STANDARD CODE BS8110 PART2 (reinforced concrete code) STATES(Unless partitions, cladding and finishes, etc. have been specifically detailed to allow for anticipated deflections, relative lateral deflection in any one storey under the characteristic (unfactored) wind load should not exceed (H/500), where H is the storey height.)But in steel structures BS5950-part1-2000 states that in multistorey buildings drift to be limited to (H/300), where H is the storey height.But bear in mind the issue above is inter-related to P-DELTA issue, as whether to have it sway or non-sway structures.The eurocode is having moreorless the same approach.But as per my experience we had approached to different projects differently depending on finishings sensitivity to movement, we used (total height/750) as per UBC and (total height /1000) for another project.So, down the road ur own judgement after assessing other disciplines requirements u can specify drift sensitivity level.
thanks and regards

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources