Hydronic calculations in a system that has a closed supply loop and a closed return loop

Hydronic calculations in a system that has a closed supply loop and a closed return loop

Hydronic calculations in a system that has a closed supply loop and a closed return loop

(OP)
I know the title of this tread is confusing but i can't think of a better way to describe it. I have an existing chilled water system where the piping has been completely looped around an area - both supply and return. The best analogy I can think of is how many compressed air systems come out of the compressor and connect to a rectangular loop as opposed to just teeing off in different directions.

I have a chilled water loop that does the same thing. The supply pipe connects to a rectangular loop, and so does the return line. I still don't think i am explaining it well. Please see attached. There are little supply and return take-offs valves all around the loop for future connection.

My question is how to do the hydronic calculations on this when everything is looped? If the pipes were not looped, I would essentially have 2 parallel branches where the 6" pipes first tee off. Everything is 6" by the way except all the little future valves.

Can I treat it as 2 parallel branches?

RE: Hydronic calculations in a system that has a closed supply loop and a closed return loop

This is a piping network problem. I know exactly how to solve it, but cannot go into detail in this post (not enough space). Perhaps the moderators can tell me how to do it by private email?

RE: Hydronic calculations in a system that has a closed supply loop and a closed return loop

I don't think piping you sketched can function at all. There is no unique path to terminal units, so network can never be balanced.

That has nothing to do with compressed air network, which is not closed loop system.

RE: Hydronic calculations in a system that has a closed supply loop and a closed return loop

First I’ll you will need to flow rates for all future taps, min &max flows and dp of the chiller to understand the system dynamics. I would treat as 2 parallel runs for piping in standard hvac use unless the first taps consume a large % of system flow. I prefer a reverse rtn but the piping cost adds up. Unlike compressible fluid flow, cross tying does not lower installed cost unless a unique need is needed such as a leg out of service, odd dp requirements of the terminal valves or no control vlv at therminals (think of a coil header). I have done this in a process with high pressures and the terminal vlv may have control issues with a DP in the main. If cost is the primary concern, go with 2 direct return legs and use dp type flow controls and flow control at the chiller with a drive.

RE: Hydronic calculations in a system that has a closed supply loop and a closed return loop

First confirm you have variable flow chiller and that you have mix of two way and 3 way chiller water flow control valve at the AHUs so the 3 way chilled water flow control valve would insure the minimum chilled water flow would bet above the minimum allowable chilled water flow. Also each AHU should have flow balancing valve.

If all AHU chilled water flow control valve are two way, provide a differential pressure control valve between supply and return to pass the minimum allowable flow when the set DP is reached.

You have to make sure you can provide enough gpm for future taps and also allow for the actual delta T across each AHU coil which may not match the chiller delta T. However the net mixed delta T of all should match the chiller delta T.

You can use 2 parallel branch but make sure you get the worst case by trial and error. Make sure you use the worst case branch to AHU pressure drop including coil, control valve, balance valve, isolation valves, strainer, fittings, pipe lengths.

Locate DP sensor to control speed of pump and determine set point.

RE: Hydronic calculations in a system that has a closed supply loop and a closed return loop

Quote from Drazen: I don't think piping you sketched can function at all. There is no unique path to terminal units, so network can never be balanced.

That has nothing to do with compressed air network, which is not closed loop system.

It turns out that it can be done. I never said it was easy though. It requires 69 non-linear equations, plus 26 linear equations for a total of 95 simultaneous equations. You would need a math program like TK Solver or MatLab to do it. Large municipal water and gas utilities do this regularly.

RE: Hydronic calculations in a system that has a closed supply loop and a closed return loop

trashcan, both water and gas utilities are open-loop systems and they make flow probability assessments to get optimum pipe diameters, aver flow condition etc., not to balance system. open systems can self-equalize to some extent when supply is connected from two sides.

using that logic in close-loop system makes no sense at all. not only that it cannot be predicted which path flow will take in different terminal units opening scenarios, but even reverse flow cannot be predicted. that is mess which does not belong to engineering practice.

RE: Hydronic calculations in a system that has a closed supply loop and a closed return loop

Go to a sprinkler dude who has the software to analyze this system.

It's not simple.

RE: Hydronic calculations in a system that has a closed supply loop and a closed return loop

I like your mark-up and you're on the right track. If branch "one" of your supply/return has higher pressure loss, "make" it shorter and branch "two" longer until you get near equal, add reasonable safety factor and size the pump. Watch that one of the take-offs doesn't have a disproportionate length. If so, that will become your index run. I'm assuming you know the flow of each tap at peak building load. What is nice about a loop is when the peak shifts, the flow can be provided from the other side which reduces required pipe size. You can also isolate a small length without taking down the whole system. Have at it!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close