Hi all,
I am currently helping a colleague to determine a ground fault that tripped one of our 13.8kV outgoing feeders. This feeder is protected by a VAMP 140 overcurrent and earth fault protection relay. Based on the how the current settings of the relay it seems that the Earth fault protection was not accurately programmed during commissioning. Therefore, we would like to verify the settings and simulate in ETAP. The feeder being protected is a 2/0kcmil, 3/C, 15kV, CU cable with a distance of about 2KM and connected to a 13.8kV/ 480V step-down transformer downstream. What we would like to know of the Earth fault settings are accurate or is requiring changes and how is this value calculated. Below is a single line diagram illustrating the system and current settings in ETAP. Phase CT ratio is 100/1 and Residual Ground CT ratio is 50/1.
In advance many thanks for your support and if additional information is required please advice.
Regards,
Jairo

RE: Io Residual current in protection relay settings

What is a type of neutral grounding of the system?
solid, low impedance, high impedance, compensated?
What is a phase to neutral fault current?

RE: Io Residual current in protection relay settings

(OP)
Thhanks for the prompt reply. The grounding is solidly grounded. I dont't understannd your second question. Can you please elaborate?

RE: Io Residual current in protection relay settings

Hello
that means, single phase short circuit current.

In your case, system is solid grounded, its very high level of single phase short circuit current.
Some one make short circuit study of system?

Im not familiar with Vamp terminals.
What is 0.67A ?
Why 0.3PU is 30A?
CT is 50/1

Phase CT is 1000/1

Something not correct.

==========
Trip of line was false trip or right trip?

RE: Io Residual current in protection relay settings

(OP)
Hi slavag,

On the single line diagram the CT ratio is not correct. It has been changes to 100/1 and the residual CT is 50/1. A short circuit study has not been made. The settings in my opinion are not correct, therefore should be determined. Is there a way to calculate these settings?

RE: Io Residual current in protection relay settings

Not sure anyone will give you a simple formula. Might be time to read up on the subject.
I am a bit confused about this I0 residual current, however. Residual current as measured by the residual current CT is equal to 3I0.

RE: Io Residual current in protection relay settings

I am confused by the pick-up settings.
As I read it, with a 50:1 CT, a pick-up at 20 Amps primary would be 0.40 PU and a pick-up at 30 Amps primary would be 0.60 PU
The first step is to determine what fault current you want to trip at and what time delay or inverse curve you want to use.
Then it is a matter of reading the relay manual to set the relay.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Io Residual current in protection relay settings

Without short circuit study....not possible determinate setting.

What is a setting for overcurrent?

RE: Io Residual current in protection relay settings

(OP)
The overcurrent settings are found in the picture below. The CT ratio used is 100/1

RE: Io Residual current in protection relay settings

(OP)
The PU provided in the image above is not correct because the CT ratio that was set into the relay is 100/1 which should be 50/1. That is the first thing I have noticed when the settings were downloaded from the relay.

RE: Io Residual current in protection relay settings

OK.
next steps.
1. What is a setting ground fault and overcurrent of upstream breaker?
2. What is a data of 13.8/0.48kV transformer?

( setting of 20A, 1sec and 30A 0.5 sec....is not setting)

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources