Existing lintel question

Existing lintel question

Existing lintel question

(OP)
I have an existing CMU lintel I have to review and it seems to just be a 16" deep bond beam, you can see in the photos they have one at mid height at the rest of the walls and there are vertical applications as well to connect columns to. The steel appears to just be to finish the jamb and header. The width is 12" CMU. Am I off base with thinking that this is just a grouted/concrete beam?

RE: Existing lintel question

It could be; that would be fairly common, but it could also be a cast-in-place header on cast-in-place jambs. I can't see any mortar joints on either the jambs or the header.

BA

RE: Existing lintel question

How do you plan to determine the size and location of steel reinforcement?

RE: Existing lintel question

(OP)
Location would just be assumed at bottom because my wall locator tool couldn't find anything (maybe due to depth of rebar into the beam from the side). Size....try to find a minimum to assume.

RE: Existing lintel question

I don't know if this is an illusion but it appears to me that there is visible deflection in the lintel.

RE: Existing lintel question


Gut feeling it is a pour on site concrete beam, maybe you'll neet to do some coring on the underside of the beam to determine amount of steel. Also you need a regular 4" core to determine concrete strength.


I also see the deflection, and not sure if there is a crack.

Cheers

RE: Existing lintel question

I'm guessing that is a cast in place concrete beam. And I think the "deflection" was probably built that way due to deflection of the formwork. The "cracks" are also probably formwork joints, so not cracks.

Don't core drill anything. Do a bit of percussion drilling to locate and not damage the bottom bars and identify them. You can't just assume a quantity of steel. Concrete strength should not be an issue.

RE: Existing lintel question

Seems like a simple metal detector ($50 variety) should be able to register some steel bars, even if not precise depth or bar size can be determined. That would concern me if you can't detect anything. If I understand you right there is a steel plate at the bottom of the beam. Maybe that is throwing off any readings but I'm curious what that is there for.
Agree with tapping around to find SOMETHING and absolutely agree you can't just assume there is steel. Wouldn't expect concrete strength to control anything as long as the visible concrete appears competent.
Curious about the deflection question. Seems like form sag could be a factor but I think I see "stair step" cracking in the block above the beam that would be consistent with beam deflection. I'd look for flexural cracking at bottom of beam midspan and maybe shear cracking (SCARY)at mid-depth of beam near the ends.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources