I have a situation where the floor

I have a situation where the floor

I have a situation where the floor

(OP)
I have a situation where the floor joist only attach to one side of a steel beam, is this going to cause problems with twisting? The floor joists are trusses and both the beam and the trusses are 16" high. The beam is 16" 40lbs per foot and is 30' long with a second floor exterior wall resting on it. Thank You

RE: I have a situation where the floor

It's an issue but, generally, a resolvable one. We'll be able to offer greatly improved advice if you supply:

1) a sketch of the truss to beam connection detail.

2) a sketch of the beam to beam support connection detail.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: I have a situation where the floor

Also provide truss spans and design loads.

RE: I have a situation where the floor

(OP)


THE PIC SHOULD BE ATTACHED
THANKS

RE: I have a situation where the floor

What kind of connection is proposed between the screw jacks and the steel beam? To be honest, there's going to be a fair bit of torsion and not a ton of hope of resolving it if it's just sitting on a pair of screw jacks. What the actual intended connection between the truss and beam.

RE: I have a situation where the floor

(OP)
Was going to use strong-tie bracket, the wood is going to be bolted to the Web of the beam.
I can change the post to what ever will work.

RE: I have a situation where the floor

Quote:

is this going to cause problems with twisting?

Yes - a Simpson hanger attached to the side of a beam will twist the beam.
If the hanger is an over-the-top type hanger (top flange hanger vs. a face mount) it will twist the beam.
The wall on top of the beam, assuming a simple stud wall, will not help (much).
The beam will twist.
The screw jack columns, with a simple bracket top plate will not be capable of resisting the beam twist.
Find a local engineer to design this if you aren't one.

Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies

RE: I have a situation where the floor

Here are a few options to help mitigate the torsion problem. My preference would be A + D. That's simple enough that somebody might actually do it as specified. You contractor will, of course, object to the lack of field adjustability in the HSS.



I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: I have a situation where the floor

(OP)
Is the 16" beam overkill? The length is 25 ft. carrying the 16' floor trusses and 2ND floor and roof. Northeast USA.

RE: I have a situation where the floor

Is the bolted connection between the truss and beam enough that you have moment fixity between the two for the offset from centreline of beam to end of truss?? If so, if you take the truss as simply supported to the centreline of the beam, what is the rotation in the truss at the centreline of beam? The beam is not going to rotate further than the truss would if this was a pure pin situation. If the connection can handle the moment generated by the offset between the end of the truss and centreline of beam, and the rotations are small, I don't see a need to change the connection. Just make sure the screw jack can handle loads being applied off centre.

RE: I have a situation where the floor

Koot's A detail may help mitigate any cold transfer issues if this is an exterior wall support.

Dik

RE: I have a situation where the floor

Detail A is my go to detail when supporting parallel chord wood trusses on steel beams.

RE: I have a situation where the floor

(OP)
Detail A looks good to me also, the only problem is the beam size is the same as the truss. Do I really need a 16" beam or can I use a shorter, heavier beam?

Thank you all!!

RE: I have a situation where the floor

FK22, the beam size should be a simple structural analysis, including torsion etc.

Please remember: we're not all guys!

RE: I have a situation where the floor

(OP)
is there a program to figure the beam?

RE: I have a situation where the floor

Quote (JAE)

Find a local engineer to design this if you aren't one.

Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources