Bearing load on concrete curb
In residential applications we often have bearing reactions from posts on relatively slim curbs (say 6" wide). The curbs are not very tall (say 18"). When calculating the capacity of the curb, is this just a bearing problem as the height is small enough that buckling is unlikely or are there other checks (side face blowout) or similar that should be checked?
RE: Bearing load on concrete curb
Also, how big a load we talking?
And any potential for uplift?
With those questions in mind, my initial guess would be a non-issue unless the loads are really high and/or there is potential uplift.
Would you assume relatively uniform bearing pressure below? This would equate to 350psi which would be well below concrete bearing stress.
I can check with some assumed lateral displacement to calc vertical bars at KootK mentioned. But would you also check a shear failure from a side bursting?
I've seen a 20° failure slope assumed for bearing ledges that then have horizontal bars designed for shear friction. Doesn't quite apply to a curb condition. Would you assume a failure plane of something similar and check the shear along that slope?
Yeah. It's mostly baloney but that's what is assumed and it seems to work out alright.
My understanding is the conventional bearing stress is the stress that you can use without concerning yourself with side bursting. Not like there's a whole lot that you could do about it in a six inch curb anyhow.
I don't know and have wondered about this myself. I've seen that same check and have never understood under what conditions the regular bearing is insufficient. Maybe it has to do with situations where you've got that lateral "N" force on the connection like with corbels.
I'll go with just bearing and take some comfort that at least 6" diameterx 12" long is used frequently for cylinder testing and those things can take some serious loads before fracturing.