Pier dowels into structural slab

Pier dowels into structural slab

Pier dowels into structural slab

(OP)
Just curious how you all align the pier dowels between a circular pier and a two-way structural slab. Do you align them splayed at 90s and lapped directly with horizontal and vertical bars or do you rotate so the dowels come at 45 degree angles relative to the horizontal and vertical bars. Any reason to do one way vs the other?

RE: Pier dowels into structural slab

(OP)
Sorry, not 45 degree angle but radially out of pier. With 4 dowels they may potentially be at 45 degrees angle from slab reinforcing.

RE: Pier dowels into structural slab

Why do you want to align the pier dowels with the slab reinforcement? Typically, I see the horizontal dowel legs equally spaced, coming out radially from the pier.

RE: Pier dowels into structural slab

I'll go with outward radial because that's really the only buildable alternative that contractors can be expected to abide by. To truly moment connect the slab to the pier, you'd want to turn the hooks into the pier and align them with the slab bars which would be awful for constructability. It is for this reason that I usually consider columns and flat plate roof/podium slabs to be pinned for the purpose of proportionimg the slab flexural steel.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: Pier dowels into structural slab

This sounds like a top-of-column condition not taking lateral loads. Detail same as rectangular. Consider column pinned at the top. I often use smaller bars (#5 say) as the dowels, 90-hooks turned inward, and lapped to the vertical pier/column bars (#9 or whatever size they are). This permits the column joint to have some moment capacity (it's never truly pinned) while providing a familiar construction detail.

RE: Pier dowels into structural slab

(OP)
Great, thanks for all the input guys. I appreciate it.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources