choice among two theories for a random winding turn failure
A random wound 460 vac motor failed by turn to turn short. Only one phase and one coil was involved.
The failed coil happened to be a line-end coil, but 25% of coils in the machine are line end coil and steep voltage surges are not expected in this power system. So we ruled out surge as a cause.
The motor had been in service about 30 years service. During inspection, it was reported some parts of winding were dry and brittle, similar to what is expected after 30 years service.
Slides 1 and 2 show overview of endwinding and failure area.
Based on inspection, two different people opined two different apparent causes of the failure.
Scenario 1 - as highlighted in slide 3, the slot fill appears low. General looseness of winding from shrinkage and/or low initial slot fill are proposed as cause of failure. Note that in slide 4 the particular coil that failed does not have same appearance of low slot fill but it is postulated that this coil moved.
Scenario 2 - as highlighted in slide 5, the coils immediately bend as they exit the slot (rather than bending a little ways outside the slot). It is enough to distort the phase paper (which makes the looseness look worse than it really is from the end, even though it is admittedly loose looking). The cause of this early bend may be result of coil forming (the slot sections are not long enough, the end span is not long enough) and it also may be a result of winding assembly process (no attempt was made to establish a bend further outside the slot prior to dip/bake). Either way it places a tremendous stress on the coil in that area, which can be aggravated by thermal changes and vibration.
Among scenario 1 or 2, which seems more likely to you?
(2B)+(2B)' ?
RE: choice among two theories for a random winding turn failure
(2B)+(2B)' ?
I suspect that this condition plus a little moisture was the cause of failure.
Why close to the slot ends?
Moisture and or condensation and tracking across the end of the stator iron.
Bill
"Why not the best?"
Jimmy Carter
I am particularly interested in discussing the relative merits of these two scenarios, neither of which is definitive of course… just the best guesses from available info.
The timing does play a role in how we view these as you say. Scenario A allows for the possibility that looseness may have gotten worse over time based on the thermal aging which was apparent during inspection. Both scenarios provide a mechanism whereby stresses from vibration are magnified so that it might take awhile for vibration to degrade the winding to the point of failure.
Regarding coil looseness, at first view it seems very loose from the photos, but then considering that the slot liners are bowed outwards abnormally, the view from the end might be deceiving in that respect. What do you think?
Attached I included photos of two other random wound motors I grabbed randomly from my files for comparison (not sister motors, not even same OEM). The first one definitely has the ideal prounounced bend well outside the slot. The second one does not (although has not failed). The looseness does not appear as severe fromo the end in either although again it may be misleading since the slot liners are not as far bent out as the failed motor
(2B)+(2B)' ?
It’s likely safe to rule out a surge as suggested because that type of failure tends to be more catastrophic in visual appearance.
The coil exiting the iron would look more severed, and have more copper bead debris like the one small one seen in your photo of the failure.
I would couple your Scenario 2 with an additional factor. “Workmanship”. It kind of looks like the motor was rewound at some point in its operating history.
A nicked wire nestled among that failed coil eventually vibrated with a neighboring conductor (helped by the loose slot fill) causing what happened.
The coil’s sharp bend exiting the iron slot can often not be avoided due to lack of physical space available within the end bracket of the motor.
The “cuffed” slot liners certainly helped provide additional protection in making the exiting formed bend.
If this type of failure occurred on a new or recently rewound motor, it could be promoted a case for warranty.
John
First, you should check the value of "volts per coil."
Such a damage occurs very often in case of random wound coils , if this value is excessive.
I suppose it is about 4 pole winding in 48 slots, but the number of parallel circuits is unknown . If this winding is done with 4 circuits for example, this could be a cause.
Winding Design and Repair
Just how long did you expect it to last!
In the real world nowadays we go for 15 to 20 years design life. Very often this is longer than the life of the plant.
Thanks, it two-circuit delta 4-pole machine. 48 slots. Phase to phase voltage dropped across 8 coils. I guess that makes it 460/8 ~ 58 volts/coil. Random wound, so of course full coil voltage could appear across physically adjacent turns. But I can't say I have ever heard of a motor failing from excess steady state turns per coil. And these motors are from a respected OEM. We have 6 of these motors and the first two failures among them occurred after approx 30 years (180 motor years) service last year and this year. We didn't take that close a look at last year's failure but looking closer at this one.
(2B)+(2B)' ?
(2B)+(2B)' ?
We have already completed our formal evaluation and put in place our corrective actions.
The actions include proactively rewinding the older motors in this family over the next several years to address age.
The reason for the question is primarily a matter of curiosity. In the back of my mind I'm also wondering whether I might be able to effectively priortize the rewinds by pulling back the endbells and looking at the endwindings to judge these conditions.
(2B)+(2B)' ?
with the information that we have been given I would have to say
"None of the above."
From the information that I have, which is mostly pictorial, I see several turns in the winding that are the color of annealed copper and appear to have the insulation completely baked off. I see several other turns with insulation that appears to have been burnt black from heat.
A single point failure tends to heat all winding conductors equally. The winding conductors in this instance seem to have not been heated by a point failure.
I see many conductors that appear to have good insulation.
I see several conductors that appear to have severe heat damage to the insulation. This damage appears to extend for several inches from the slot end.
I see several conductors that appear to have the insulation completely burnt off and the copper annealed by excess heat.
These may all be indications of a turn to turn short internal to the coil.
The heat developed by shorted turns eventually led to damage to the slot liner and flashover.
I understand that your plant runs ungrounded. That would explain the relatively little arcing damage to the stator.
Based on the information that you have given I have to say that the likely hood of either of the scenarios causing that damage is so ow that I have to reply;
Based on the available information the motor has been in service for 30 years. Those conditions have not caused a failure for the first 40 years.
I have to reply;
Other information that may not have been given enough consideration.Surges have been ruled out.
BUT I understand that this may be an ungrounded system.
You may have a high impedance, discontinuous ground fault or an intermittent high impedance, discontinuous ground fault.
Discontinuous ground faults have been known to superimpose high voltage high frequency potentials on ungrounded system.
The fault may be steady but it may also be a transient related to switching and/or motor starting.
A common feature of this type of fault is random motor burnout throughout the plant.
A common feature of this type of failure is winding turn failure near the line end of the winding.
I do not have enough information to rule this possibility out, and this may be much more likely than either scenario #1 or #2.
This type of failure may often initiate turn to turn shorts buried in the coil bundle. From the pictures this may have been a possibility.
Pete, my friend, please take a walk around the plant to cool off before you flame we with your response.
Respectfully.
Bill
"Why not the best?"
Jimmy Carter
(2B)+(2B)' ?
Neither one.
The heat damage to the windings may not be consistent with either guess.
The other slots don't seem to show any damage from low fill.
Other tight bends don't seem to show any damage.
My discussion of the relative merits of these two scenarios is that they don't have much merit.
A suggestion that may save some money. We had some generators severely damaged by being flooded by salt water during hurricane Mitch. We were able to wash, dip and re-bake the generator windings for a saving of thousands of dollars. depending on your evaluation of motors for future rewind, this may save some money particularly on larger sized motors.
Respectfully.
Bill
"Why not the best?"
Jimmy Carter
Both mechanisms can degrade the strand insulation over time. We can get many individual strands damaged before a turn fault occurs (it takes two strands damaged at the same location for turn to turn fault). There is no time limit for these conditions to result in failure. Furthermore as noted the looseness seen today may certainly be worse than it was initially. And if I'm trying to decide whether inspecting for looseness is effective it matters not whether the looseness was there initially or got worse over time.
The heat damage is entirely consistent with a turn to turn short.
I don't expect to see any other damage... all the visible damage unique to that coil appears to have occurred after the turn to turn short. After the first turn to turn short motor tends not to last very long so I don't expect to see any other turn to turnh shorts in the same motor.
Failure analysis is certainly not an exact science but again I have gotten the best available input based on a lot more than what was presented here. I'm not expecting anyone to have the clarvoyance to know the cause of failure from those photos. It was a simple question. Please take it at face value.
(2B)+(2B)' ?
(2B)+(2B)' ?
Walt
(2B)+(2B)' ?
I was wondering: How sure are you that surges were essentially absent? Do you have some kind of scans on the voltages?
George
"When you go looking for problems, you will find them... But they may not be the problems you went looking for!"
Of the two scenarios I have to choose #1. In my opinion both are weak and probably not directly related to the failure. I'm not concerned with voids in the slot however if strands are loose that could be a contributing factor. Have to checked/monitored the THD?
Why do you say these scenarios are weak?
I'm not sure I see the distinction between the empty space we see from end of the slot and potential looseness of the strands in the slot.... they seem roughly the same thing to my thinking. Perhaps good resin can overcome low slot fill to some extent.
Have not checked/monitored THD in voltage or current on this particular equipment. There are no power electronics feeding the motor nor directly fed from the same load center transformer. Have not seen any significant voltage distortion during the times we have had an opportunity to monitor voltage on similar 480 volt systems in our plant. Have seen some significant distortion on current for some motors running at low load. Voltage does run on the high side from time to time but never more than 10% above nameplate.
I appreciate the interest, but I'll repeat I did not ask the forum to help figure out the cause. I asked to discuss relative merits of two scenarios.
(2B)+(2B)' ?