Dental Clinic Peninsula Sink
Dental Clinic Peninsula Sink
(OP)
I am currently interning, so forgive any informality, and am trying to layout waste and vent plan for a dental clinic with sinks on a peninsula with no accessible wall for vent piping near by. I have included a screen shot of the situation and lengths, i was aware that a 2" vent pipe could go a max of 8' to a wall. I am not certain, but doubt i can go to the wall in the middle. Any advice would be helpful and ask any questions that I did not cover.





RE: Dental Clinic Peninsula Sink
RE: Dental Clinic Peninsula Sink
If you do not have a wall nearby, you can do a combination waste and vent if you size the drain piping larger. In the International Plumbing Code, look in Chapter 9, around Section 912.
RE: Dental Clinic Peninsula Sink
Keep in mind that even though code has a limit on the distance between the trap and the vent, it is pretty generous. In Int'l Plumbing Code, see Table 909.1.
Dental chairs/sinks frequently come as packaged units and only require the most basic utility connections (water, vacuum, drain). Getting and studying equipment cut sheets are essential in generating proper plumbing system designs.
PS) yellow text on white is very difficult to read, impossible for some. Recommend avoiding in the future
RE: Dental Clinic Peninsula Sink