Why do we have some motors star and some delta wound in marine application with same line voltage?
Why do we have some motors star and some delta wound in marine application with same line voltage?
(OP)
Why do we have some motors star and some delta wound in marine application with same line voltage?





RE: Why do we have some motors star and some delta wound in marine application with same line voltage?
RE: Why do we have some motors star and some delta wound in marine application with same line voltage?
Your answer:
1 It depends.
2 It doesn't matter, unless you intend to use star/delta starting. Star delta starting will only work on the lower of the two motor rated voltages.
NEMA (North American) motors tend to be 9 lead motors, either star or delta, suitable for series or parallel connection and a voltage ratio of 2:1 Star is more common.
IEC motors tend to be 6 lead motors suitable for either star or delta connection with a 1.73:1 voltage ratio.
Bill
--------------------
"Why not the best?"
Jimmy Carter