Earth Fault Protection for Ungrounded Wye Primary of Transformer

Earth Fault Protection for Ungrounded Wye Primary of Transformer

Earth Fault Protection for Ungrounded Wye Primary of Transformer

(OP)
Would the residually connected CT's work for ground faults if the neutral is ungrounded for Yd11 transformer?

RE: Earth Fault Protection for Ungrounded Wye Primary of Transformer

No.

RE: Earth Fault Protection for Ungrounded Wye Primary of Transformer

Slightly longer answer - the only means of detecting a ground fault on that system will be using voltage.

RE: Earth Fault Protection for Ungrounded Wye Primary of Transformer

Ground faults where? If the source is grounded and it is feeding the Y winding then you could detect a fault on the Y winding with 3 CT's. That would be known as balanced earth fault protection where I am from. More details required.
Regards
Marmite

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources