Transfer beam modelling analysis and design
Transfer beam modelling analysis and design
(OP)
I have a building where a transfer beam is required at a lower level to allow for the removal of some columns for vehicular access.
My first attempt is a single span beam over two bays but my problem in modelling is to cope with the end moments which arise in the columns as the columns won't be able to large moments?
I can reduce the column stiffnesses to shed some of the moment back to the beam or design the beam for the full simply supported moment but not sure what the correct response is?
My first attempt is a single span beam over two bays but my problem in modelling is to cope with the end moments which arise in the columns as the columns won't be able to large moments?
I can reduce the column stiffnesses to shed some of the moment back to the beam or design the beam for the full simply supported moment but not sure what the correct response is?






RE: Transfer beam modelling analysis and design
http://www.nceng.com.au/
"Programming today is a race between software engineers striving to build bigger and better idiot-proof programs, and the Universe trying to produce bigger and better idiots. So far, the Universe is winning."
RE: Transfer beam modelling analysis and design
RE: Transfer beam modelling analysis and design
- capacity design a a flexural hinge into the top of the column and design the column for the associated hinge moment.
- post tension the beam.
Frankly, if you're having this problem, I take it as evidence of your transfer beam not being stiff enough. Attempting to fix that by softening and potentially weakening your column seems sketchy to me.
I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
RE: Transfer beam modelling analysis and design
RE: Transfer beam modelling analysis and design
1) you have to be much more careful in considering the sequential nature of the construction and;
2) this might just spread the floor height problem over multiple floors. That said, extra floor height above grade is usually cheaper than extra floor height below grade. It can work well if the lower floors of the building already have high ceilings for mixed use occupancies and the beams can fit within the plenum space.
I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
RE: Transfer beam modelling analysis and design