Does a standard for 400Kv nominal class equipment exist in North America? If I use 400Kv I must either use IEC equipment or 500Kv IEEE/ANSI equipment?

RE: 400Kv Equipment

Not that I've ever heard of. You're talking phase to phase right?

RE: 400Kv Equipment

(OP)
Correct, phase to phase.

RE: 400Kv Equipment

No, IEEE/ANSI does not have a 400 kV class. There is 345kV and then 500kV.

RE: 400Kv Equipment

(OP)
Thanks :) What is set official the max operating voltage rating of 345kv equipment?

RE: 400Kv Equipment

362 kV or 5% over nominal. See ANSI C84.1.

RE: 400Kv Equipment

(OP)
Thanks. And my research yields that there is no such thing is a 400kv (IEC) dead tank breaker?

RE: 400Kv Equipment

Gas insulated dead tank breakers certainly exist at 400kV, and well above. Siemens, ABB, Alstom (now GE Grid) all have dead tank designs.

RE: 400Kv Equipment

(OP)
Just not in IEEE designs?

RE: 400Kv Equipment

Well, they're sold over here with IEC / EN certification, CE Marked and type approved by the big European utilties. They're quite possibly designed in Switzerland (ABB Hosag) or Germany (Siemens), regardless of the eventual market. 400kV is a standard transmission voltage in the UK.

RE: 400Kv Equipment

(OP)
And most of the world :D The thing is in North America 400Kv is unheard of, its either 345 (362) kv or 500 (550) kv. No 420kv rated equipment. In the UK you have post and tube bus work in substations?

RE: 400Kv Equipment

We have a lot of legacy 275kV open terminal substations in the UK, but most newer substations at 275kV and 400kV are gas insulated because of the greatly reduced size. Retrofits of the legacy 275kV sites as they are uprated to 400kV also tend to install GIS.

RE: 400Kv Equipment

(OP)
How does GIS compare to open bars? Id imagine its more in the long run?

RE: 400Kv Equipment

If you have the land for Air Insulated, it will less expensive than GIS, but if you don't have/can't buy the land then GIS becomes the preferred option. We've used GIS at 115kV where we've needed more station than we have yard for.

RE: 400Kv Equipment

As David says - lack of space for 400kV gear, and precious little prospect of obtaining it. Elimination of the ancillary plant associated with legacy air blast gear is another attraction.

RE: 400Kv Equipment

(OP)
You still holding on to them or replacing them with SF6?

RE: 400Kv Equipment

Air blast gear? The outdoor 275kV air blast breakers from the 1960's are being replaced with indoor 400kV GIS as the transmission voltage is increased.

RE: 400Kv Equipment

(OP)
Yup, air blast. But the 132kv equipment is still remaining as open air bus?

RE: 400Kv Equipment

(OP)
One request if I may, would anyone happen to have links to these 400Kv dead tank breakers? I keep looking but I am only finding live tank versions.

RE: 400Kv Equipment

Dead tank circuit breaker are quite uncommon in western Europe and, generally speaking, in the all the countries using 400 kV for power transmission.
Note that, due to the recent harmonization of IEC & ANSI/IEEE Standards for High-voltage Circuit-breakers, most EHV circuit breakers can be nowadays installed both in IEEE and IEC market areas.
As a consequence most producers have not developed a 420 kV class dead tank circuit breaker, as it should have a marginal market share.
However, ABB has recently launched a 420 kV class hybrid switchgear, which in its most simple declination consists in a dead tank circuit breaker. We have installed some of these in a similar fashion to dead tank circuit breakers.
https://library.e.abb.com/public/3c1693cf1d451352c...

Si duri puer ingeni videtur,
preconem facias vel architectum.

RE: 400Kv Equipment

(OP)
Thanks. What about live tank breakers make them attractive in Europe and most IEC countries? Is it cost alone?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources