ABB REM620 Thermal Overload Function Test Reset Problem
2

ABB REM620 Thermal Overload Function Test Reset Problem

ABB REM620 Thermal Overload Function Test Reset Problem

(OP)

Hi friends ,

I m relay engineer. I m at substation now. During testing thermal overload test , I couldnt reset the thermal degree...Waiting to be zero ( degree) takes much time .

I disabled the function but still same..I just want to test from zero.

Rated Current : 1,00
Initial thermal val : 74 %

Setting Group 1 :

Overload Factor : 1,05
Alarm thermal value : 85 %
Restart thermal value : 40 %
Negative Seq Factor : 0
Weighting factor : 50 %
Time constant normal : 320 s
Time constant start : 320 s
Time constant stop : 500 s
Env temperature mode : FLC only
Env tepmperature Set : 40 C


Thanks

RE: ABB REM620 Thermal Overload Function Test Reset Problem

Page 343 of the technical manual says:
The time to lockout release is calculated, that is, the calculation of the cooling time to a
set value. The calculated temperature can be reset to its initial value (the Initial
temperature setting) via a control parameter that is located under the clear menu. This
is useful during testing when secondary injected current has given a calculated false
temperature level.

So, first you need to change your "Initial thermal val" setting to 0 and save. Then you need to push the clear button on the relay, scroll down to the proper setting and clear it.

https://library.e.abb.com/public/3fed1ac90f340a76c...

RE: ABB REM620 Thermal Overload Function Test Reset Problem

(OP)
Thank you for your answer...

I read the manual ..I think I coulndt see that point.

Again thanks much :)

RE: ABB REM620 Thermal Overload Function Test Reset Problem

(OP)
" JG2828 " , by the way I checked the manual ,There s calculation of trip time.

toperate= -T . In [( Qfinal-Qoperate)/(Qfinal/Qn)]

Is it possible to use that calculation for my function ( MPTTR ) ? And dont understand ( Qfinal and Qn )
IF isnt , do you know the calculation ?

Thanks

RE: ABB REM620 Thermal Overload Function Test Reset Problem

rayas91,
I don't have an answer to that one. Hopefully someone else can chime in.

Thanks.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources