How would I calculate the Kjoule thermal capacity for a rotor starter.

Rotor current=1805A
Rotor Voltage = 1335V
Stator voltage= 11000V
Stator current=243.1A
Motor rating 4000kW
3 phase Y
cos 0.89
Starting torque 200%

RE: Thermal capacity of liquid resistance started motor

Since kJoule=kWattsecond, the time needs to be given or estimated. Some idea about the motor prospective acceleration curve would help.

RE: Thermal capacity of liquid resistance started motor

(OP)
The run up time for the liquid resistance starter is 10 seconds.

RE: Thermal capacity of liquid resistance started motor


Possibly applicable discussion/links at Thread237-24735
  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources