Solid Earthed Neutral of Delta Wye(Star) Transformer
Solid Earthed Neutral of Delta Wye(Star) Transformer
(OP)
I am working in SE Asia to provide 1500kVA 11kV/380V step down delta wye(star) transformers as part of the electrical distribution.
Earthed neutral in the secondary side of Tx is required as a code requirement.
There is a debate about whether it is necessary to provide PVC sheath conductor or just bare conductor for the earthed neutral (i.e. from the star point to the earth electrode)
My view is that the star point should be zero current and voltage under normal condition. The use of Bare conductor (for example tinned cu. tape)should have no problem.
However, when there is say earth fault, how can we provide proper earth fault setting so that automatic disconnection can be provided and the person who get in touch with the bare conductor will not get fatal electric shock.
Any advice? or a PVC sheath conductor should be adopted?
Earthed neutral in the secondary side of Tx is required as a code requirement.
There is a debate about whether it is necessary to provide PVC sheath conductor or just bare conductor for the earthed neutral (i.e. from the star point to the earth electrode)
My view is that the star point should be zero current and voltage under normal condition. The use of Bare conductor (for example tinned cu. tape)should have no problem.
However, when there is say earth fault, how can we provide proper earth fault setting so that automatic disconnection can be provided and the person who get in touch with the bare conductor will not get fatal electric shock.
Any advice? or a PVC sheath conductor should be adopted?






RE: Solid Earthed Neutral of Delta Wye(Star) Transformer
What about physical protection of the ground lead? What would happen if it were to become disconnected?
Ground leads can become damaged, or stolen, and if that is a possibility, it needs to be protected.
Another thought is to paint or cover it so it does not look like copper.
RE: Solid Earthed Neutral of Delta Wye(Star) Transformer
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Solid Earthed Neutral of Delta Wye(Star) Transformer
RE: Solid Earthed Neutral of Delta Wye(Star) Transformer
We still have a ungrounded Y transformer feeding a delta system in a location where we can't get a good ground (rock).
The ungrounded X0 bushing is used for neutral shift detection.
So for the few applications that are ungrounded, they are special, And I don't recommend it unless it is well thought out.
In fact in some countries there 240V to homes is ungrounded, but that has some interesting problems.
RE: Solid Earthed Neutral of Delta Wye(Star) Transformer
The netural point will be directly earthed via cu. tape to the earth electrode to from a TT earthing system in my case.
Earth Fault Protection will be provided. Is it correct to assume that if prospective earth fault can trigger the earth fault protection in a very short period then it can be justified?
RE: Solid Earthed Neutral of Delta Wye(Star) Transformer
RE: Solid Earthed Neutral of Delta Wye(Star) Transformer
RE: Solid Earthed Neutral of Delta Wye(Star) Transformer
In my part of the country, the ground wire on a pole mounted distribution transformer may be as small as #6 AWG.
It is generally insulated.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Solid Earthed Neutral of Delta Wye(Star) Transformer
It is doubtful that the two will be in reach of each other.
RE: Solid Earthed Neutral of Delta Wye(Star) Transformer
Also you may require an additional neutral to case bond for the transformer.
A good review of NEC Article 250 could yield you the proper answers.
RE: Solid Earthed Neutral of Delta Wye(Star) Transformer
RE: Solid Earthed Neutral of Delta Wye(Star) Transformer
You're ignoring ground electrode resistance. You can easily get nearly full line voltage on the ground electrode conductor in open neutral conditions with TN-C (combined earth/nuetral).