Function of DPCV in FCU/AHU valve package

Function of DPCV in FCU/AHU valve package

(OP)
What is the function of DPCV in FCU/AHU valve package?. which is the appropriate location to install in valve package?

RE: Function of DPCV in FCU/AHU valve package

DPCV? Differential pressure Control valve? FCU/AHU? Fan coil/Air handler? You need to do a little more explaining on your question please.

RE: Function of DPCV in FCU/AHU valve package

There is many types of balancing control valve.
You might want to get someone in the field to explain you about this. Suppliers / AC contractor/ Engineers, etc.

But simple answer for your simple question,
What is important for AHU / FCU is the chilled water flowrate required for the cooling.
So one way to control it by control the differential pressure to give correct flowrate required. CHW flowrate will modulate according to the heat load required in the A/C space.
To install at the return side of the CHW pipe (leaving CHW pipe, after the AHU / FCU).

ps:
I have my first post in eng-tips. Yay

RE: Function of DPCV in FCU/AHU valve package

Function - to control water flow rate to either a fixed flow rate or variable depending on cooling load required ( probably controlled on exit temperature)

Position? Upstream or downstream of the unit. downstream means you won't run into air problems, but upstream could reduce pressure if this is what is required.


Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

RE: Function of DPCV in FCU/AHU valve package

As others have stated, your question is too vague to answer the proper application. A delta P valve is intended to replace a control valve and a balance valve in a 2 way application. One must review the application from a system level not just a single terminal. These valves can be used on heating or cooling coils but one need the primary pumping design information for a proper selection. These will work with variable pumping designs. Most commonly found on leaving side of coil. I would use caution on an application of limited retrofit due to unknown system flow rate and coil dp on other terminals.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close