(OP)
We've had some failures of control circuits of dahlander motors. I believe it was as result of someone fiddling with delay off timer to ensure high speed to low speed does not occur unless motor has first come to standstill.
I'd like to find an authoritative write up of this issue, textbook or link to website/literature that anyone is aware of? Or if someone has the time to develop a good discussion of the problem.
Maybe I'm not using correct search terms but i'm googled out!
apart from finding hits to other eng-tips threads on problems with these motors (which has been valuable) the best i could find was this http://www.moeller.net/binary/schabu/SB2011-8_onli...
From other links i'm aware motor runs as generator and negative slip.
is it a case that a more robust motor (if specified) could tolerate this under worse case conditions, i got that impression reading the eaton stuff.
In our case We are seeing failure of terminations on bottom of high speed contactor (happened on two separate fan starters) and in another case terminations of motor terminal box.
Not discounting poor installing and joints, as it is fairly new system, but the fact that there is rumour of timer being changed at some point makes me think this could be reason. No record of timer setting to compound matters but Ive told them to check the run down time from high speed mode.
I'd like to find an authoritative write up of this issue, textbook or link to website/literature that anyone is aware of? Or if someone has the time to develop a good discussion of the problem.
Maybe I'm not using correct search terms but i'm googled out!
apart from finding hits to other eng-tips threads on problems with these motors (which has been valuable) the best i could find was this http://www.moeller.net/binary/schabu/SB2011-8_onli...
From other links i'm aware motor runs as generator and negative slip.
is it a case that a more robust motor (if specified) could tolerate this under worse case conditions, i got that impression reading the eaton stuff.
In our case We are seeing failure of terminations on bottom of high speed contactor (happened on two separate fan starters) and in another case terminations of motor terminal box.
Not discounting poor installing and joints, as it is fairly new system, but the fact that there is rumour of timer being changed at some point makes me think this could be reason. No record of timer setting to compound matters but Ive told them to check the run down time from high speed mode.





RE: Dahlander motor - high to low speed
RE: Dahlander motor - high to low speed
Muthu
www.edison.co.in
RE: Dahlander motor - high to low speed
The common factor._
The same crew of inexperienced installers did both installations.
This was new work in both cases.
An experienced electrician will tighten his cable connections and then attempt to twist the cable in the terminal or connector. This will tend to straighten the strands and the connection will loosen. The connection may then be easily tightened more. The twisting-tightening process may be repeated two or three time before the connection is truly tight.
Seven strand cable is the worst case.
As a demonstration, I have asked electricians to tighten a connection on seven strand cable as tight as they could and then I have given the cable a twist and dropped the cable out of the connector.
Multiple failures may be the result of improperly tightened connections.
Too long a time setting between high and low speed should not be a problem.
Too short a time setting between high speed and low speed, may cause an electrical issue but also may cause damage to driven machinery.
It depends.
Hoisting equipment is a special case.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Dahlander motor - high to low speed
RE: Dahlander motor - high to low speed
Also time setting between low and high speed is one second.
Good luck !
RE: Dahlander motor - high to low speed
My suspicion here, given the description of it being CONTROL system failures that you are experiencing, is that the application IS automatically changing speeds or stepping through them, but there is no transitional timer. So the controls are relying solely on the mechanical interlocks and aux contacts associated with them. That will work when brand new, but as the components age, the slight changes in timing as a result of mechanical wear can have detrimental and progressively worsening consequences.
"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington
RE: Dahlander motor - high to low speed
The example of Panter (to see above) 2MW motor, Dahlander connection, it means "0.5MW/2,0MW motors" (1 to 4 power ratio if variable torque/Y-YY connection)L/H speeds -typically fans/pumps. This is the reason of a tachometer interlock - more safe than a simple time delay. A "500kW motor" trying to reduce the speed of a load that was accelerated by a "2000 kW motor" without any form of control it is not a good idea.
edison123@"Dahlander windings are meant for changing from one speed to another on the fly. Why would one want them to start from zero speed?" A typical application is the ventilation fans of diesel engine rooms off shore vessels that depends of ambient conditions. It can be Man/Auto switched from 0 to Low speed, 0 to High speed (better if in 2 steps), L to H, H to L (idle time with tach supervision or time delay) L to 0, H to 0. Other intentional delays are refining of design. Hope it helps.