simple frame analysis by stiffness matrix approach
hi, i am analysing a simple frame structure - composed of a horizontal beam and a vertical column (the frame looks like '7' with 6 dofs restrained at the bottom of column)... i have prepared the stiffness matrix for the strcture, now need to prepare the force matrix..... i need to analyse the structure only for the dead weight and wish to know how to consider the weight of column in the force matrix. understand that the beam weight can be applied as momement and vertical shear at the beam ends, how to consider the column weight - is is just applied as equal point loads at the top and bottom ? thanks
RE: simple frame analysis by stiffness matrix approach
I have a question for you though, as I am also trying to develop a similar program using another language (not Fortran). Are you trying to make your program be able to output complete shear, moment and deflection diagrams for all your elements? Or just nodal forces and displacements?
regarding my pgrm,i have not decided what all to extract as output. if your worry is about plotting the outputs, u cud use libraries from softwares like plplot/gnplot etc... they sync with fortran/python etc
Place W at the bottom node and find the maximum axial load in the column. To find the axial load elsewhere on the column, simply subtract the weight of column between the point in question and the bottom node.
BA
Just as the other distributed loads are applied as a equivalent shear and moments I would think one would do the same for a vertical member. If you then look at your final output (axial, shear, moment diagrams) you should have an axial load that increases linearly from top to bottom, due to the distributed dead weight along its length.
To check you work create an equivalent model in STAAD or RISA and compare with your own program, that is the only way I was able to work the bugs out of my own programming and to finally arrive at the correct output.
I'm sure you already have it but a copy of Structural Analysis by Hibbeler was very helpful.
A confused student is a good student.
Nathaniel P. Wilkerson, PE
www.medeek.com
BA
I've done this and found the post-processing to be quite a bit more difficult than the matrix stuff. Let me know if there's anything that I can do to help with your project.
CODE -->
############################################### # # Sub Routines for Truss Designer (FINK TRUSS MATRIX) # ############################################### ######################## # # Rigid Peak Joint # ######################## sub Matrix { ############################## # # Overhang Loading and Graphs # ############################## if($Overhang > 0) { $Moment_overhang = ($Tctl_pli*$Overhang*$Overhang)/2; $Moment_overhang_out = sprintf("%.1f", $Moment_overhang); $Lgtoverhang = $Overhang/(cos($Phi)); $coefaover = -1*($Tctl_pli/2) * cos($Phi) * cos($Phi); $coefaoverv = -1*($Tctl_pli) * cos($Phi) * cos($Phi); $coefaovera = $Tctl_pli * sin($Phi) * cos($Phi); $coefaover_out = sprintf("%.1f", $coefaover); $coefaoverv_out = sprintf("%.1f", $coefaoverv); $coefaovera_out = sprintf("%.1f", $coefaovera); @momentsoverlist = (); @xoverlist = (); $Y_axisover = ""; $X_axisover = ""; $Y_axisoverv = ""; $Y_axisovera = ""; $Eqn_momentover = 'Overhang: M(x) = ' . "$coefaover_out" . 'x^2'; $Eqn_shearover = 'Overhang: V(x) = ' . "$coefaoverv_out" . 'x'; $Eqn_axialover = 'Overhang: A(x) = ' . "$coefaovera_out" . 'x'; for ($xover = 0; $xover < $Lgtoverhang; $xover +=.5) { $Momentoverx = $coefaover * $xover**2; $Shearoverx = $coefaoverv * $xover; $Axialoverx = $coefaovera * $xover; push (@momentsoverlist, $Momentoverx); push (@xoverlist, $xover); $Y_axisover .= "$Momentoverx,"; $Y_axisoverv .= "$Shearoverx,"; $Y_axisovera .= "$Axialoverx,"; $X_axisover .= "\"$xover\","; } # Add point at panel point $xover = $Lgtoverhang; $Momentoverx = $coefaover * $xover**2; $Shearoverx = $coefaoverv * $xover; $Axialoverx = $coefaovera * $xover; push (@momentsoverlist, $Momentoverx); push (@xoverlist, $xover); $Maxm_over_out = sprintf("%.1f", $Momentoverx); $Maxv_over_out = sprintf("%.1f", $Shearoverx); $Maxa_over_out = sprintf("%.1f", $Axialoverx); $Y_axisover .= "$Momentoverx"; $Y_axisoverv .= "$Shearoverx"; $Y_axisovera .= "$Axialoverx"; $X_axisover .= "\"$xover\""; } else { $Moment_overhang = 0; $Overhang_graphs_html = ""; } #################################### # # DISTRIBUTED LOADS MATRIX ANALYSIS # #################################### ############################ # # Known External Loads (Qk) # ############################ $Shear1 = $Shear4 = $Tctl_pli*$L12*.5; $Shear2 = $Shear3 = $Tctl_pli*$Ltcp*.5; $Moment1 = $Moment4 = ($Tctl_pli*$L12*$L12)/12; $Moment2 = $Moment3 = ($Tctl_pli*$Ltcp*$Ltcp)/12; $Shear5 = $Shear7 = $Bctl_pli*$L17*.5; $Shear6 = $Bctl_pli*$Lbcp*.5; $Moment5 = $Moment7 = ($Bctl_pli*$L17*$L17)/12; $Moment6 = ($Bctl_pli*$Lbcp*$Lbcp)/12; $Moment1_neg = $Moment4_neg = -1*$Moment1; $Moment2_neg = $Moment3_neg = -1*$Moment2; $Moment5_neg = $Moment7_neg = -1*$Moment5; $Moment6_neg = -1*$Moment6; $Q1 = 0; $Q2 = -1*($Shear1 + $Shear2); $Q3 = $Moment1 - $Moment2; $Q4 = 0; $Q5 = -1*($Shear2 + $Shear3); $Q6 = $Moment2 - $Moment3; $Q7 = 0; $Q8 = -1*($Shear3 + $Shear4); $Q9 = $Moment3 - $Moment4; $Q10 = 0; $Q11 = -1*($Shear5 + $Shear6); $Q12 = $Moment6 - $Moment5; $Q13 = 0; $Q14 = -1*($Shear6 + $Shear7); $Q15 = $Moment7 - $Moment6; $Q16 = 0; $Q17 = ($Moment4 + $Moment5) - $Moment_overhang; $Q18 = -1*($Moment1 + $Moment7) + $Moment_overhang; $Qk_matrix = Math::MatrixReal->new_from_string(<<"MATRIX"); [ $Q1 ] [ $Q2 ] [ $Q3 ] [ $Q4 ] [ $Q5 ] [ $Q6 ] [ $Q7 ] [ $Q8 ] [ $Q9 ] [ $Q10 ] [ $Q11 ] [ $Q12 ] [ $Q13 ] [ $Q14 ] [ $Q15 ] [ $Q16 ] [ $Q17 ] [ $Q18 ] MATRIX $Qk_matrix_out = sprintf("%s", $Qk_matrix); ################################# # # Superimposed Loading TC and BC # ################################# $q1super_matrix = Math::MatrixReal->new_from_string(<<"MATRIX"); [ 0 ] [ $Shear1 ] [ $Moment1 ] [ 0 ] [ $Shear1 ] [ $Moment1_neg ] MATRIX $q2super_matrix = Math::MatrixReal->new_from_string(<<"MATRIX"); [ 0 ] [ $Shear2 ] [ $Moment2 ] [ 0 ] [ $Shear2 ] [ $Moment2_neg ] MATRIX ################################### # # Corrected Superposition Matrices # ################################### $Shear1new = $Tctl_pli*$L12*.5*cos($Phi); $Axial1new = $Tctl_pli*$L12*.5*sin($Phi); $Moment1new = $Moment1; $Moment1_negnew = $Moment1_neg; $Shear2new = $Tctl_pli*$Ltcp*.5*cos($Phi); $Axial2new = $Tctl_pli*$Ltcp*.5*sin($Phi); $Moment2new = $Moment2; $Moment2_negnew = $Moment2_neg; $q1super_matrix = Math::MatrixReal->new_from_string(<<"MATRIX"); [ $Axial1new ] [ $Shear1new ] [ $Moment1new ] [ $Axial1new ] [ $Shear1new ] [ $Moment1_negnew ] MATRIX $q2super_matrix = Math::MatrixReal->new_from_string(<<"MATRIX"); [ $Axial2new ] [ $Shear2new ] [ $Moment2new ] [ $Axial2new ] [ $Shear2new ] [ $Moment2_negnew ] MATRIX ################################### $q3super_matrix = Math::MatrixReal->new_from_string(<<"MATRIX"); [ 0 ] [ $Shear3 ] [ $Moment3 ] [ 0 ] [ $Shear3 ] [ $Moment3_neg ] MATRIX $q4super_matrix = Math::MatrixReal->new_from_string(<<"MATRIX"); [ 0 ] [ $Shear4 ] [ $Moment4 ] [ 0 ] [ $Shear4 ] [ $Moment4_neg ] MATRIX $q5super_matrix = Math::MatrixReal->new_from_string(<<"MATRIX"); [ 0 ] [ $Shear5 ] [ $Moment5 ] [ 0 ] [ $Shear5 ] [ $Moment5_neg ] MATRIX $q6super_matrix = Math::MatrixReal->new_from_string(<<"MATRIX"); [ 0 ] [ $Shear6 ] [ $Moment6 ] [ 0 ] [ $Shear6 ] [ $Moment6_neg ] MATRIX $q7super_matrix = Math::MatrixReal->new_from_string(<<"MATRIX"); [ 0 ] [ $Shear7 ] [ $Moment7 ] [ 0 ] [ $Shear7 ] [ $Moment7_neg ] MATRIX ########################### # # Known Displacements (Dk) # ########################### $Dk_matrix = Math::MatrixReal->new_from_string(<<"MATRIX"); [ 0 ] [ 0 ] [ 0 ] MATRIX $Dk_matrix_out = sprintf("%s", $Dk_matrix); $Matrix_email_output2 = qq{ Qk = $Qk_matrix_out Dk = $Dk_matrix_out }; ########################################### # # Structure Stiffness Matrices for Members # ########################################### %k1map = (1 => 20, 2 => 21, 3 => 18, 4 => 1, 5 => 2, 6 => 3); %k2map = (1 => 1, 2 => 2, 3 => 3, 4 => 4, 5 => 5, 6 => 6); %k3map = (1 => 4, 2 => 5, 3 => 6, 4 => 7, 5 => 8, 6 => 9); %k4map = (1 => 7, 2 => 8, 3 => 9, 4 => 16, 5 => 19, 6 => 17); %k5map = (1 => 10, 2 => 11, 3 => 12, 4 => 16, 5 => 19, 6 => 17); %k6map = (1 => 13, 2 => 14, 3 => 15, 4 => 10, 5 => 11, 6 => 12); %k7map = (1 => 20, 2 => 21, 3 => 18, 4 => 13, 5 => 14, 6 => 15); %k8map = (1 => 13, 2 => 14, 3 => 15, 4 => 1, 5 => 2, 6 => 3); %k9map = (1 => 13, 2 => 14, 3 => 15, 4 => 4, 5 => 5, 6 => 6); %k10map = (1 => 10, 2 => 11, 3 => 12, 4 => 4, 5 => 5, 6 => 6); %k11map = (1 => 10, 2 => 11, 3 => 12, 4 => 7, 5 => 8, 6 => 9); %Thetax = (1 => $Phi, 2 => $Phi, 3 => -$Phi, 4 => -$Phi, 5 => 0, 6 => 0, 7 => 0, 8 => 3.14159265358 - $Alpha, 9 => $Beta, 10 => 3.14159265358 - $Beta, 11 => $Alpha); %Area_hash = (1 => $A12, 2 => $A23, 3 => $A34, 4 => $A45, 5 => $A56, 6 => $A67, 7 => $A17, 8 => $A27, 9 => $A37, 10 => $A36, 11 => $A46); %Inertia_hash = (1 => $Ix12, 2 => $Ix23, 3 => $Ix34, 4 => $Ix45, 5 => $Ix56, 6 => $Ix67, 7 => $Ix17, 8 => $Ix27, 9 => $Ix37, 10 => $Ix36, 11 => $Ix46); %Length_hash = (1 => $Lgt12, 2 => $Lgt23, 3 => $Lgt34, 4 => $Lgt45, 5 => $Lgt56, 6 => $Lgt67, 7 => $Lgt17, 8 => $Lgt27, 9 => $Lgt37, 10 => $Lgt36, 11 => $Lgt46); if (($E12) && ($E17) && ($E27) && ($E37)) { %E_hash = (1 => $E12, 2 => $E12, 3 => $E12, 4 => $E12, 5 => $E17, 6 => $E17, 7 => $E17, 8 => $E27, 9 => $E37, 10 => $E37, 11 => $E27); } else { %E_hash = (1 => 1500000, 2 => 1500000, 3 => 1500000, 4 => 1500000, 5 => 1500000, 6 => 1500000, 7 => 1500000, 8 => 1500000, 9 => 1500000, 10 => 1500000, 11 => 1500000); } %Lambdax = (); %Lambday = (); %T_matrix_hash = (); %TT_matrix_hash = (); %kprime_matrix_hash = (); %k_matrix_hash = (); %k_assembly_matrix_hash = (); $K_matrix = new Math::MatrixReal(21,21); for ($Membernum = 1; $Membernum <= 11; $Membernum +=1) { $lmdx = $Lambdax{"$Membernum"} = cos($Thetax{"$Membernum"}); $lmdy = $Lambday{"$Membernum"} = sin($Thetax{"$Membernum"}); $lmdy_neg = $lmdy * -1; ######################################### # # Displacement Transformation Matrix (T) # ######################################### $T_matrix = Math::MatrixReal->new_from_string(<<"MATRIX"); [ $lmdx $lmdy 0 0 0 0 ] [ $lmdy_neg $lmdx 0 0 0 0 ] [ 0 0 1 0 0 0 ] [ 0 0 0 $lmdx $lmdy 0 ] [ 0 0 0 $lmdy_neg $lmdx 0 ] [ 0 0 0 0 0 1 ] MATRIX $T_matrix_out = sprintf("%s", $T_matrix); $T_matrix_hash{"$Membernum"} = $T_matrix; $Matrix_email_output2 .= qq{ T$Membernum = $T_matrix_out }; ##################################### # # Force Transformation Matrix (TT) # ##################################### $TT_matrix = new Math::MatrixReal(6,6); $TT_matrix->transpose($T_matrix); $TT_matrix_out = sprintf("%s", $TT_matrix); $TT_matrix_hash{"$Membernum"} = $TT_matrix; $Matrix_email_output2 .= qq{ TT$Membernum = $TT_matrix_out }; ##################################### # # Member Stiffness Matrix (k') # ##################################### $AE_L = ($Area_hash{"$Membernum"} * $E_hash{"$Membernum"})/$Length_hash{"$Membernum"}; $EI12_LLL = (12 * $Inertia_hash{"$Membernum"} * $E_hash{"$Membernum"})/($Length_hash{"$Membernum"})**3; $EI6_LL = (6 * $Inertia_hash{"$Membernum"} * $E_hash{"$Membernum"})/($Length_hash{"$Membernum"})**2; $EI4_L = (4 * $Inertia_hash{"$Membernum"} * $E_hash{"$Membernum"})/($Length_hash{"$Membernum"}); $EI2_L = (2 * $Inertia_hash{"$Membernum"} * $E_hash{"$Membernum"})/($Length_hash{"$Membernum"}); $AE_L_neg = $AE_L * -1; $EI12_LLL_neg = $EI12_LLL * -1; $EI6_LL_neg = $EI6_LL * -1; if ($Membernum >= 8) { $kprime_matrix = Math::MatrixReal->new_from_string(<<"MATRIX"); [ $AE_L 0 0 $AE_L_neg 0 0 ] [ 0 0 0 0 0 0 ] [ 0 0 0 0 0 0 ] [ $AE_L_neg 0 0 $AE_L 0 0 ] [ 0 0 0 0 0 0 ] [ 0 0 0 0 0 0 ] MATRIX } else { $kprime_matrix = Math::MatrixReal->new_from_string(<<"MATRIX"); [ $AE_L 0 0 $AE_L_neg 0 0 ] [ 0 $EI12_LLL $EI6_LL 0 $EI12_LLL_neg $EI6_LL ] [ 0 $EI6_LL $EI4_L 0 $EI6_LL_neg $EI2_L ] [ $AE_L_neg 0 0 $AE_L 0 0 ] [ 0 $EI12_LLL_neg $EI6_LL_neg 0 $EI12_LLL $EI6_LL_neg ] [ 0 $EI6_LL $EI2_L 0 $EI6_LL_neg $EI4_L ] MATRIX } $kprime_matrix_out = sprintf("%s", $kprime_matrix); $kprime_matrix_hash{"$Membernum"} = $kprime_matrix; $Matrix_email_output2 .= qq{ k'$Membernum = $kprime_matrix_out }; ##################################### # # Global Member Stiffness Matrix (k) # ##################################### $k_matrix = ($TT_matrix * $kprime_matrix) * $T_matrix; $k_matrix_out = sprintf("%s", $k_matrix); $k_matrix_hash{"$Membernum"} = $k_matrix; $Matrix_email_output2 .= qq{ k$Membernum = $k_matrix_out }; ####################################################### # # Global Member Stiffness Matrix (Assembly) (k padded) # ####################################################### $kmap_name = 'k'."$Membernum".'map'; %kmap = %{$kmap_name}; $k_assembly_matrix = new Math::MatrixReal(21,21); for ($ith = 1; $ith <= 6; $ith +=1) { $rowmap = $kmap{"$ith"}; for ($jth = 1; $jth <= 6; $jth +=1) { $colmap = $kmap{"$jth"}; $kvalue = $k_matrix->element($ith,$jth); $k_assembly_matrix->assign($rowmap,$colmap,$kvalue); } } $k_assembly_matrix_out = sprintf("%s", $k_assembly_matrix); $k_assembly_matrix_hash{"$Membernum"} = $k_assembly_matrix; $Matrix_email_output2 .= qq{ k$Membernum Assembly = $k_assembly_matrix_out }; ################################ # # Structure Stiffness Matrix (K) # ################################ $K_matrix = $K_matrix + $k_assembly_matrix; } $K_matrix_out = sprintf("%s", $K_matrix); $Matrix_email_output2 .= qq{ K Structure Stiffness Matrix = $K_matrix_out }; ############################# # # K11 Matrix (K11) # ############################# $K11_matrix = new Math::MatrixReal(18,18); for ($ith = 1; $ith <= 18; $ith +=1) { for ($jth = 1; $jth <= 18; $jth +=1) { $K11value = $K_matrix->element($ith,$jth); $K11_matrix->assign($ith,$jth,$K11value); } } $K11_matrix_out = sprintf("%s", $K11_matrix); #print qq{<br>$K11_matrix_out}; $Matrix_email_output2 .= qq{ K11 Matrix = $K11_matrix_out }; ############################# # # K21 Matrix (K21) # ############################# $K21_matrix = new Math::MatrixReal(3,18); for ($ith = 19; $ith <= 21; $ith +=1) { $ith21 = $ith - 18; for ($jth = 1; $jth <= 18; $jth +=1) { $K21value = $K_matrix->element($ith,$jth); $K21_matrix->assign($ith21,$jth,$K21value); } } $K21_matrix_out = sprintf("%s", $K21_matrix); $Matrix_email_output2 .= qq{ K21 Matrix = $K21_matrix_out }; ############################# # # K11INV Matrix (K11 Inverse) # ############################# $K11INV_matrix = $K11_matrix->decompose_LR->invert_LR; $K11INV_matrix_out = sprintf("%s", $K11INV_matrix); $I_matrix = $K11_matrix * $K11INV_matrix; $I_matrix_out = sprintf("%s", $I_matrix); $Matrix_email_output2 .= qq{ K11 Inverse Matrix = $K11INV_matrix_out Indentity Matrix Check = $I_matrix_out }; ############################# # # Du Matrix (Du) # ############################# $Du_matrix = $K11INV_matrix * $Qk_matrix; $Du_matrix_out = sprintf("%s", $Du_matrix); $Matrix_email_output2 .= qq{ Du Matrix = $Du_matrix_out }; ############################# # # Qu Matrix (Qu) # ############################# $Qu_matrix = $K21_matrix * $Du_matrix; $Qu_matrix_out = sprintf("%s", $Qu_matrix); $Matrix_email_output2 .= qq{ Qu Matrix = $Qu_matrix_out }; #################################### # # Displacement Matrix (D = Du + Dk) # #################################### $DuT_matrix = new Math::MatrixReal(1,18); $DuT_matrix->transpose($Du_matrix); $DkT_matrix = new Math::MatrixReal(1,3); $DkT_matrix->transpose($Dk_matrix); $DT_matrix = $DuT_matrix . $DkT_matrix; $D_matrix = new Math::MatrixReal(21,1); $D_matrix->transpose($DT_matrix); $D_matrix_out = sprintf("%s", $D_matrix); $Matrix_email_output2 .= qq{ D Matrix = $D_matrix_out }; #################################### # # Internal Loading of Members (q) # #################################### %D_member_matrix_hash = (); %q_matrix_hash = (); %qmod_matrix_hash = (); for ($Membernum = 1; $Membernum <= 11; $Membernum +=1) { $kmap_name = 'k'."$Membernum".'map'; %kmap = %{$kmap_name}; $D_member_matrix = new Math::MatrixReal(6,1); for ($ith = 1; $ith <= 6; $ith +=1) { $rowmap = $kmap{"$ith"}; $kvalue = $D_matrix->element($rowmap,1); $D_member_matrix->assign($ith,1,$kvalue); } $D_member_matrix_out = sprintf("%s", $D_member_matrix); $D_member_matrix_hash{"$Membernum"} = $D_member_matrix; $q_matrix = ($kprime_matrix_hash{"$Membernum"} * $T_matrix_hash{"$Membernum"}) * $D_member_matrix; $q_matrix_out = sprintf("%s", $q_matrix); $q_matrix_hash{"$Membernum"} = $q_matrix; if ($Membernum =~ /^[1234567]$/) { # $q1super_matrix $super_matrix_name = 'q'."$Membernum".'super_matrix'; $qsuper_matrix = ${$super_matrix_name}; $qmod_matrix = $qsuper_matrix + $q_matrix; $qmod_matrix_out = sprintf("%s", $qmod_matrix); $qmod_matrix_hash{"$Membernum"} = $qmod_matrix; $Matrix_email_output_full .= qq{ D$Membernum = $D_member_matrix_out q$Membernum = $q_matrix_out q$Membernum (mod) = $qmod_matrix_out }; $Matrix_email_output .= qq{ q$Membernum (mod) = $qmod_matrix_out }; } else { $Matrix_email_output_full .= qq{ D$Membernum = $D_member_matrix_out q$Membernum = $q_matrix_out }; $Matrix_email_output .= qq{ q$Membernum = $q_matrix_out }; } } # TEST AND DEBUG CODE #$Matrix_email_output .= join("\n", %Thetax); #$Matrix_email_output .= join("\n", %Lambdax); #$Matrix_email_output .= join("\n", %Lambday); $Matrix_email_output .= join("\n", %E_hash);A confused student is a good student.
www.medeek.com
www.medeek.com
That will work for finding the forces in a determinant structure, but it won't give the right answer for deflections or for forces in an indeterminant structure.
The procedure for a stiffness analysis is:
- For each member find the fixed end actions for all applied loads
- Calculate the node deflections due to these end actions
- Calculate the reactions at the supports
- Knowing the support reactions, calculate the actions along each member, taking account of distributed loads, including self weight.
The axial fixed end forces for the self weight of a vertical member are +-W/2.Doug Jenkins
Interactive Design Services
http://newtonexcelbach.wordpress.com/
BA
Where the column meets the ground (column bottom) this appears to be zero degrees of freedom at this node. Since this is the case no external forces or moments are placed at this node. At the other reaction point it appears your have a pin joint so only rotational degree of freedom is present. Based on your diagram your global displacement matrix should have 5 rows and your global loading matrix 4 rows.
There is no external lateral force so that entry in your loading matrix will be zero. The vertical load at node 2 will be Wb/2 + Wc/2, the other two entries in the loading matrix will be the moments at each end of the beam (with opposite signs).
www.medeek.com
If you want the program to output the correct reactions, why would you not place external forces and moments at a node having zero degrees of freedom?
BA
When you work out the support reactions you of course need to add in the fixed end actions at the supports.
Medeek - I think the horizontal member in the original post is a free cantilever, so there are 6 degrees of freedom, but if it was a pinned connection there would be 4 degrees of freedom, so 4 rows in the load matrix as well.
Doug Jenkins
www.medeek.com