Bus bar sizing
Bus bar sizing
I need to calculate what size bus bar is required for a 2000 kW generator with a 3000 amp 100% rated breaker. I have in stock some 4 in by 1/4 in thk copper, and would like to use it if possible. What is the equation I should use? Any help would be appreciated.
RE: Bus bar sizing
1. Fink D. G., Carroll J. M. "Standard Handbook for Electrical Engineers," 10th Edition, McGraw-Hill, Inc., 1968
pages 10-116 and 10-117, Section 429 "Flat Bars,"
Figure 10-165 (Reflects Amperes versus number of laminations per bus). It appears that your copper bars will fit the bus-bar arrangement L for 3000A
_ _
|_| |_|
_ _ <- Space 2 3/4"
|_| |_|
Space 2 3/8"
RE: Bus bar sizing
1.- Is the bus bar for use in a switchgear or are you in need to expand the generator breaker housing for easiness of power cable connection.
2.- Be sure to calculate your temperatures and short circuits forces to correctly establish support locations.
If you are doing something outdoors then you might need to perform some added calcs.
RE: Bus bar sizing
The intent is to mount a side car to the pothead and place the breaker in the side car. We need to extend the generator's bars over to the breaker. The distance should not be longer than 20-25 inches. This will be an indoor unit.
RE: Bus bar sizing
The above mentioned figure is relevant to bus bars for 60Hz/sec and the ampacity is for alternating current carrying capacity of bus bars for 35°C rise in still unconfined air. If there are deviations, appropriate revisions shall be applied. Please, notice that buses are traditionally installed with long dimensions in the vertical direction. This is to clarify squares in my posting.
RE: Bus bar sizing
RE: Bus bar sizing
http://busbar.copper.org/ampacity/busbar.htm
RE: Bus bar sizing
RE: Bus bar sizing
Thanks for the infor on the busbar site-good data
RE: Bus bar sizing