HVAC exhaust air temperature?

HVAC exhaust air temperature?

(OP)
I'm wondering what the typical temperature range of a multi-story office building or hotel's HVAC exhaust air is.

I’m also interested in the volumetric flow rate, but I assume that more widely varies depending on the size of the system. I'm specifically looking at 7 to 8-story buildings in a fairly densely packed city in Europe.

RE: HVAC exhaust air temperature?

HVAC exhaust? Like toilet room air, or relief air? Either way I would assume the exhaust would be dependent upon the room air being exhausted. If the room is set to 21C then I would not assume 70C exhaust air.

RE: HVAC exhaust air temperature?

(OP)
From an exhaust vent on the roof?

RE: HVAC exhaust air temperature?

There is no general rule here, you will have to measure it.

RE: HVAC exhaust air temperature?

Exhaust air should be equivalent or slightly higher than your room setpoint.

knowledge is power

RE: HVAC exhaust air temperature?

Or are you referring to the refrigeration condenser exhaust temperature?

Keith Cress
kcress - http://www.flaminsystems.com

RE: HVAC exhaust air temperature?

Exhaust would be the amount of exhaust from all the toilets connected to the exhaust system. Temperature would be the temperature resulting from the mix of toilet exhaust from rooms with AC on (occupied rooms) and that from unoccupied rooms (say 80 to 85 F) and if you want the temperature of exhaust at fan discharge, add fan heat (fan only or including motor heat if motor is within airstream). You can measure by taking velocity traverse readings on sectional areas of the discharge opening and averaging corresponding traverse temperature measurements. You can have a certified air balancing contractor perform this.Why do you need this information?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close