Paralleling multiple safety relief devices for a pressure vessel

Paralleling multiple safety relief devices for a pressure vessel

(OP)
When (a) a relief valve is paralleled with a rupture disk / another relief valve is it acceptable to use the same pressure vessel vessel nozzle with a branch in the piping (with piping size suitably selected, of course) or is it necessary to use separate vessel nozzles to attach each relief device?

RE: Paralleling multiple safety relief devices for a pressure vessel

I assume you mean 2 x 100% capacity redundancy. It depends on the risk analysis. If the risk is acceptable to you and your company for the common cause failure of the nozzle, then yes it is acceptable. If not, then it is not. For example, it may be acceptable in a clean, solvent-like chemical service, but it may not be acceptable in a pluggage-prone polymer service.

Good luck,
Latexman

To a ChE, the glass is always full - 1/2 air and 1/2 water.

RE: Paralleling multiple safety relief devices for a pressure vessel

(OP)
Thanks @Latexman

Yes, I did mean 2x100% capacity redundancy.

But out of curiosity, would your recommendation be any different had the paralleling been for other reasons. e.g. Multiple relief scenarios, or split capacity etc.

RE: Paralleling multiple safety relief devices for a pressure vessel

Hello Plantprowler,

It is permissible to have a single nozzle serving two relief valves, or even have them on the process piping. Check API RP 520 part II- Installation of pressure relieving devices; which includes typical layouts. The key design parameter is the allowable pressure drop in the inlet piping. For a conventional relief valve, the inlet losses must be no more than 3% at full flow to avoid "chattering" of the relief valve.

best wishes,
SShep

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close