hi every one can u tell me about energy meter that what would happen if we use one phase
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: energy meter
In theory, it should measure the energy on each phase and then give a sum of the energy used. But I can't say if that will be true in practice without meter details.
RE: energy meter
Dan - Owner
http://www.Hi-TecDesigns.com
RE: energy meter
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: energy meter
RE: energy meter
The basic rule of metering is that you need N-1 elements to meter accurately. N being the number of current carrying conductors.
I have seen this rule violated by persons who were not aware of the rule.
There are accepted three phase schemes which are capable of working with N-2 elements. However these schemes depend on an assumption that the phase voltages and phase angles are equal. I have inherited systems where N-2 metering was used on a system where the voltages and angles were not equal. The result was inaccurate metering. The solution was to replace the meters with meters meeting the N-1 rule.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: energy meter
RE: energy meter
If we're talking about utility revenue meters, this is not correct.
RE: energy meter
I think that you are asking 'can a normal 3-phase digital power meter be used for a 1-phase application'.
If that is what you are asking, then the answer is yes.
I did exactly that last year,on a small 75kVA 240/120V 1-phase service, with a PML-7350 meter. I sure that other meters can be configured to work on 1-phase services as well.
Good luck.
RE: energy meter
This connection is included in the Westinghouse "Meter and Instrument Transformer Application Guide".
The connection uses delta connected CTs.
I had not used this connection before and lacked confidence.
Most revenue metering connection errors will result in a fairly large error, 2:1, 1/3, 2/3, 1/1.73, 2/1.73.
The load was mostly three phase motors but included fairly well balanced single phase loads also.
I temporarily installed a single phase meter in an out of the way location.
I checked the meter readings every couple of weeks for a few months. The single phase meter was tracking at 1/3 of the three phase meter within a couple of percent.
This gave me the confidence that I had been lacking.
Footnote;
This connection assumes that the phase voltages and phase angles are equal.
At a later date we lost one phase of our submarine cable to the Island. A replacement single conductor cable was laid parallel and a couple of feet away from the original twisted trefoil cable.
The dissimilar impedances upset our voltage and phase angle balances such that we were no longer able to meter accurately with two element meters. We replaced our two element meters with three element meters and restored metering accuracy.
On the other hand I have seen single phase meters used in an attempt to meter services derived from two phases of a three phase supply.
The meter accurately measures the consumption of any 208 Volt loads but under meters the consumption of 120 volt loads at a factor of 208/2:120 or 0.866
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: energy meter
Dan - Owner
http://www.Hi-TecDesigns.com
RE: energy meter
1> Use two phases of the meter.
2> Use one phase of the meter, one CT and route L1 and L2 through the CT in opposite directions.
Applying the current sensor to one leg of the 240 Volts will not accurately meter 120:240 Volt circuits.
Bill
--------------------
"Why not the best?"
Jimmy Carter