current transformer's, overload

current transformer's, overload

current transformer's, overload

(OP)
What danger's can arise from putting to small of C.T in circuit. We have a motor rated at over 300A full load but only have 250/5 amp current transformers. will these do until we can get the right size.
thanks
greg

RE: current transformer's, overload

A CT used for metering or protective relays should be sized for the FLA of the circuit. That being said, the difference you mention should not result in any significant damage from overheating. You didn't say if the CT was for metering or protection. If the CT is used for protection, relays commonly have tap settings above the rated 5A secondary current. If for analog metering, the meter is typically sized for the CT(250:5A CT, 250A max scale meter), and the meter may be damaged from over-scale readings.

RE: current transformer's, overload

Greg,

If th motor rated current happens to be 300A, it is quite likely that the motor would be drawing less than that (typically 80%) during normal running conditions at full load.

The CTs have thermal rating that is typically 120% (Refer IEC 60044-1) of rated current. Hence, your 250/5A rated CT should not pose any problem if loaded to 300A for some time.

Trust you find the above useful.

RE: current transformer's, overload


Some CTs have a rating factor of 1.33 at 30°C.  In a pinch, you may be able to add turns to the secondary, if the usual 10kVBIL insulation does not need preservation.  The ammeter would have to be rescaled accordingly.  Depending on duty, the meter may very well get repeatedly pegged during startup.
  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources