Long distance pulse signal to Plc
Hi All
We have materials handling application with a run of 500m maximum out to a photoelectric sensor/photo eye which is being used as an underspeed sensor. The sensor will be wired from the field to a PLC input via 30 core SWA PVC/PVC control cable untwisted and unshielded.
The sensor will detect the rotation of the non-driven pulley of a conveyor and be used to detect a problem with the conveyor where the motor might be running but the conveyor isn't moving.
The pulse frequency we are expecting from the photo electric sensor is a maximum of 4Hz.
What I am concerned about is the capacitance between cores in this cable, and from core to armour, effectively slowing the rise time of our pulses and causing problems.
I am trying to find capacitance values for the 30 core SWA PVC/PVC cable to calculate rise times, etc, but manufacturer's dont publish this data for normal PVC/PVC control cables.
Also I am having a hard time understanding the mechanisms for determining the capacitance. For example:
1) I am happy that the capacitance from one core to others increases with the number of cores, but how to quantify this based on data for core to core capacitiance? Consider the capacitances in parallel?
2) Does the presence of armor make the capacitance worse?
The closest data I have found for a 30 core SWA PVC control cable has a capacitiance value of 380nF/m which is very very high and I am not sure it is accurate
Sorry for the long post guys I hope someone can help out and that the responses help others in future
Cheers
Cheers
RE: Long distance pulse signal to Plc
This assumes a constant decision point.
TTFN
FAQ731-376: Eng-Tips.com Forum Policies forum1529: Translation Assistance for Engineers
If the sensor is 24V out I would think it could drive this 500 m cable at 4 hz without problem. Determine the output drive capability of the sensor in milli ampere and calculate the time to charge the cable with it using I= C(Dv/Dt)
Benta
I agree that 380nf/m sounds high
Since I wrote this post I've found that most proximity switch manufacturers say that you can extend the wiring 200m max - their reasons are:
1) Excessive capacitance increasing rise/fall times (they quote a maximum value of 20-100nF)
2) Too much capacitance in the output causes the capacitance to be discharged through the transistors which is an accumulative heating affect which eventually damages the electronics
3) Volt drop, interference
So I am leaning towards a proxy with the built in evaluation of the under speed, as has been suggested.